[RE-wrenches] Metal roof/self taping screws

Sindelar Solar Allan at sindelarsolar.com
Sat Oct 17 11:14:08 EDT 2020


Jay,

I researched this years ago, so I have no specific figures for you such 
as pullout strength, only the general lesson that I learned. The pullout 
strength of Tek and similar self-tapping screws is surprisingly high, 
especially in the larger diameters, such as #14, which equates to 1/4" 
as I recall. As long as the purlin into which you're drilling and 
threading is of sufficient thickness to resist deforming and tearout 
(your 3/16" should be sufficient), the screw will not tear out under 
more-than-normal wind loading.

You should be able to find actual values via online research, as I did.

Allan

On 10/17/2020 8:11 AM, Jay wrote:
> What do people recommend for a metal roof ( with flat sections, not corrugated)on 3/16” thick x 2” wide C channel for attaching L feet
>
> Self taping fasteners would be the easiest. Doing a nut and bolt would be possible but quite time consuming.
> A machine self taping bolt and then adding a nut would be a lot easier than nut and bolt.
>
> But that is my question. Is a self taping screw enough or does it need to be bolted?
>
> Jay
> Peltz power
-- 

*Allan Sindelar*
allan at sindelarsolar.com <mailto:allan at sindelarsolar.com>
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201017/ab80f3bb/attachment.htm>


More information about the RE-Wrenches mailing list