[RE-wrenches] Disconnects for "ungrounded" arrays
Chris Sparadeo
sparadeo.chris at gmail.com
Thu Oct 8 18:11:58 EDT 2020
Hi Howie,
NEC 2020 states in 690.13(E): “The PV system disconnecting means shall
simultaneously disconnect the PV system conductors that are not solidly
grounded from all conductors or other wiring systems”.
Sounds to me like there is no change to this requirement.
Best,
Chris
On Thu, Oct 8, 2020 at 5:59 PM Howie Michaelson <Howie.Michaelson at gmail.com>
wrote:
> Hi Guys,
> I seem to recall hearing at a workshop maybe 18 months ago, that NEC 2020
> was changing the string disconnect requirements for ungrounded arrays,
> changing from the need to break both the positive and negative legs of a
> string, to just one leg. This might have been specific to strings with
> optimizers, but now I cannot find my notes on this topic. Am I just
> wishful thinking here?
> Thanks,
> Howie
>
> *Howie Michaelson**Sun Catcher*
>
> *NABCEP Certified Solar PV Installer™*
>
> *Solar Electric Systems Sales & Service802-272-0004*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
Chris Sparadeo
C_802-369-4458
H_802-728-3059
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201008/e2389bd9/attachment.htm>
More information about the RE-Wrenches
mailing list