[RE-wrenches] Commercial three phase inverter @208V

Chris Mason cometenergysystems at gmail.com
Fri Sep 18 16:54:33 EDT 2020


The actual system I am proposing is 1 x 200KW and 1 x 50KW on another
building so I am thinking 5 x 50KW Core 1 inverters.

On Fri, Sep 18, 2020 at 4:36 PM Matt Partymiller <matt at sesre.com> wrote:

> Three Core 62s with a transformer is a great solution.  Lots of Fronius
> 15s could work but you could buy a backup transformer for the difference.
> Contact me off-list if you need help finding transformers.  SMA will also
> direct you to some good solutions if pressed.
>
>
>
> Matt
>
>
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Chris Mason
> *Sent:* Friday, September 18, 2020 4:04 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* [RE-wrenches] Commercial three phase inverter @208V
>
>
>
> I'm bidding a commercial rooftop of about 200KW using string inverters.
> The voltage is 208V 3Ph 60Hz, and I can't find an inverter over 15KW. I was
> hoping to use the SMA 50KW CORE 1 but everything is 480V. Any leads on a
> reputable inverter?
>
>
>
> --
>
> Chris Mason
>
> Solar systems designer
>
> Generac Generators Industrial technician
>
>
>
> Comet Systems Ltd DBA Comet Solar
> Anguilla Cell  264.235.5670
>
> WhatsApp 264.235.5670
>
> Skype: netconcepts
>
> www.cometsolar.com <http://www.cometenergysystems.com/>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200918/603ae744/attachment.htm>


More information about the RE-Wrenches mailing list