[RE-wrenches] Commercial three phase inverter @208V

Matt Partymiller matt at sesre.com
Fri Sep 18 16:35:59 EDT 2020


Three Core 62s with a transformer is a great solution.  Lots of Fronius 15s could work but you could buy a backup transformer for the difference.  Contact me off-list if you need help finding transformers.  SMA will also direct you to some good solutions if pressed.

Matt


From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Chris Mason
Sent: Friday, September 18, 2020 4:04 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] Commercial three phase inverter @208V

I'm bidding a commercial rooftop of about 200KW using string inverters. The voltage is 208V 3Ph 60Hz, and I can't find an inverter over 15KW. I was hoping to use the SMA 50KW CORE 1 but everything is 480V. Any leads on a reputable inverter?

--
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com<http://www.cometenergysystems.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200918/4943aa54/attachment.htm>


More information about the RE-Wrenches mailing list