[RE-wrenches] Cable Tray Marking

Martin Herzfeld findsolar at herzfeld.org
Thu Sep 3 15:22:27 EDT 2020


1.  In addition, there's a conflict of signal words for
NEC 110.21(B) Field-Applied Hazard Markings."Where caution, warning, or
danger signs or labels are required by this Code, the labels shall meet the
following requirements ..."  In other words, one signal word is DANGER and
the other signal word is WARNING.  Simply, DANGER *will* result in ... and
WARNING *could* result in ...

2.  Specifically, in NEC 2020 690.31(D)(2) the signal word of WARNING" was
*removed* and does not now appear to conflict?  In California, 2017
NEC/2019 CEC 690.31(G)(3) still has the WARNING signal word.  By the way,
NEC 392.18(H) refers to 110.21(B).

BTW, more information ANSI Z535 is found here:
https://webstore.ansi.org/standards/nema/ansiz5352011r2017-1668874

All the best,

Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
10037
Contract Training Provider (CTP)
Adjunct Professor, Energy - Since 2016

California Solar & Electrical Contractor License  #00833782  C46, C10, D56,
D31, C-7 - Since 2004
Solar, Electrical, Trenching, Pole Installation & Maintenance,
Instrumentation

Contract Solar (PV) Technical Inspector - 3rd Party Inspections
Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
OSHA-Authorized Construction Trainer #32-0105338
CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG

* Professional Member, International Association of Electrical Inspectors
#7035507 - Since 2006
* Accredited and Registered North American Board of Certified Energy
Practitioners (NABCEP) Continuing Education (CE) Training Provider


On Thu, Sep 3, 2020, 5:53 AM Rebekah Hren <rebekah.hren at gmail.com> wrote:

> This is interesting, since the definition of high voltage was changed to
> >1000V a few code cycles ago and it is somewhat consistently applied
> throughout the NEC at that voltage (except for workspace clearances...er).
> It seems this 392.18 label requirement could cause confusion and should be
> changed to apply to >1000V circuits.  However, the definition of high
> voltage only applies with Article 490 , Equipment >1000V so the Article 392
> Cable Tray folks can do what they want in terms of where they require high
> voltage labeling. I haven't done any research on the history of this
> labeling requirement.
>
>
> Corey maybe you would be willing to make a public input to change where
> the label is required to >1000V circuits, thus there would be no
> conflict with 690 since PV DC circuits in or on buildings cannot be >1000V.
> Due Sept 10!
>
> 490.2 Definition.
>
> The definition in this section shall apply only within this article.
> High Voltage.
>
> A potential difference of more than 1000 volts, nominal.
>
> Thanks for bringing this up Corey!
>
>
> On Thu, Sep 3, 2020 at 12:36 AM Ray <ray at solarray.com> wrote:
>
>> This is interesting, because we were considering cable trays, too.  My
>> guess is that both requirements would apply.  Picky, but I don't see that
>> 690 exempts the requirements of 392. One is for PV, one is for over 600 v.
>> Some code iteration in the future might have combined language for PV over
>> 600 v " Danger - High Voltage Photovoltaic Source - Keep Away"  and of
>> course that's so verbose that the average Joe is just going to stick his
>> paws in there anyway.....
>>
>> Ray Walters
>> Remote Solar
>> 303 505-8760
>>
>> On 9/2/20 7:54 PM, Corey Shalanski wrote:
>>
>> Wrenches,
>>
>> I am curious about the marking requirements for cable trays containing PV
>> source/output circuits rated over 600 volts, installed on a building:
>>
>>
>> NEC 392.18(H) requires a permanent, legible warning notice carrying the
>> wording “DANGER — HIGH VOLTAGE — KEEP AWAY” at least once every 10 ft.
>>
>> NEC 690.31(G)(3) requires a label or marking with the wording "WARNING:
>> PHOTOVOLTAIC POWER SOURCE" at least once every 10 ft.
>>
>> Does the 690.31 label take precedence? Are there any situations where
>> both labels would be required (or recommended)?
>>
>> --
>> Corey Shalanski
>> Jah Light Solar
>> Portland, Jamaica
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200903/b04e8065/attachment.htm>


More information about the RE-Wrenches mailing list