[RE-wrenches] Puzzle: Dryer does not work during FXR battery charging

Chris Schaefer chris at solarandwindfx.com
Sat Aug 15 12:38:36 EDT 2020


My bet is these clients are on a budget given the battery voltage and small
inverters. So there probably isn't any PV at the moment. I've been coming
across a lot of these types of systems lately. Came across a Generac 120v,
6kw Eco Gen with 3,500 hours on it! Ouch and the clients just won't add PV.
Yet they pay a gen service company to come out once a month and service the
unit on top of propane cost.

Christopher

On Sat, Aug 15, 2020 at 12:18 PM Dave Angelini Offgrid Solar <
offgridsolar at sti.net> wrote:

> Ouch ! 2812 inverter. As a pro, you need to get them away from 12V IMHO.
>
> A home with appliances needs 24v and 4kw, both minimum.
>
> As Kent said, for now you can't do both gen charging and drying clothes.
> Why do you need a genset this time of year?
>
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
> e-mail  offgridsolar at sti.net <offgridsolar at sti.net>
> text 209 813 0060*
>
> On Sat, 15 Aug 2020 11:06:26 -0400, Matt Sherald <matt at getpimby.com>
> wrote:
>
> Hello All,
>
> My curiosity was piqued by a recent customer complaint.  I'm hoping
> someone has bumped up against this issue before.
>
> The customer has a OB FXR2812 and a 3,000W Honda gen.
> Her gas clothes dryer runs just fine off the OB inverter.
> It runs properly on the Honda gen (when the inverter is bypassed)
> It will not run when the gen is on and battery charging is taking place.
>
> All the other AC loads (including the washing machine) run properly during
> battery charging with the gen.
> The OB inverter replaced an old Trace unit.  The dryer worked as it should
> with the Trace during battery charging.
>
> Any thoughts are greatly appreciated.  Thanks in advance!
>
> --
> Matt Sherald
> PIMBY Energy, LLC
> NABCEP Certified Solar PV Installer®
> 304-704-5943
>
> www.getpimby.blogspot.com
> www.getpimby.com
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 

Chris Schaefer’s
<http:www.solarandwindfx.com>

*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
<http://www.solarandwindfx.com> ~ E-mail: chris at solarandwindfx.com
<chris at solarandwindfx.com>*


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200815/df896b6f/attachment.htm>


More information about the RE-Wrenches mailing list