[RE-wrenches] Ampacity Ratings for Different Conductors

Ray ray at solarray.com
Wed Aug 12 15:25:04 EDT 2020


Also, welding and automotive cables use totally different rating systems 
like SAE, that are much more liberal than NEC.  For instance, golf carts 
are traditionally wired with #6 battery cables, and can see a continuous 
draw of 125 A and surges to 200. We would never do that by NEC, but the 
cables just get warm to the touch in golf carts.

Ray Walters
Remote Solar
303 505-8760

On 8/11/20 6:04 PM, Kent Osterberg wrote:
> Peter,
>
> The 210-amp rating is probably for a 105°C insulation temperature in 
> free air. For comparison, #2 THHN (90°C) copper in free air is rated 
> for 190 amps. Not sure that it makes sense to use a free-air rating in 
> a small closed box.  For outside use a temperature de-rating for 
> ambient temperature, maybe around -10%, should be included too.
>
> It looks like Cotek recommends a minimum cable size of 1/0, so out of 
> fear of starving the inverter of enough voltage, I wouldn't use any 
> smaller.
>
> Kent Osterberg
> Blue Mountain Solar
>
> On 8/11/2020 3:18 PM, petertor at pobox.com wrote:
>> I have been designing a off-grid system that can fit in an 
>> outside-accessible compartment with an approximate 24" square 
>> footprint and space above about 18" - 24".
>>
>> I am using two Battle Born LiFePO4 batteries rated at 24 V / 50 Ah, a 
>> Cotek pure sine wave inverter with an output power of 4,000 VA , a 
>> MorningStar TS-MPPT-60 charge controller, a Victron BMV-712 "coulomb 
>> counter" and a Battle Born surge limiter CL500.
>>
>> The current limiter limits the current to 120 continuous, and 200 A 
>> for 30 sec.
>>
>> I have been able to fit everything in and I am designing the cabling, 
>> and here is my problem.
>>
>> I have one vendor that recommends Ancor brand Tinned Marine Grade 
>> Battery Cable. It is "resistant to salt water, battery acid, oil, 
>> gasoline, heat, abrasion and ultra-violet radiation. Exceeds UL 1426, 
>> ABYC and US Coast Guard Charter boat (CFR Title 46) standards. 
>> Highest quality ultra-flexible (Type 3) tinned copper stranding. 
>> Vinyl insulation. -50 deg-C to 105 deg-C." 2 AWG is composed of 665 
>> ea 30 AWG stands.
>>
>> The same vendor has "welding cable" with an EPDM insulation rated at 
>> 600 V, water/chemical/grease/abrasion resistant, -50 deg-C to 105 
>> deg-C, "marine grade". Not UL listed. 624 ea 30 AWG strands.
>>
>> Roughly comparable pricing.
>>
>> They claim both 2 AWG cables are rated at 210 A. Not sure if this is 
>> continuous duty or whether I should derate this for what will be 
>> continuous duty.
>>
>> This is new territory for me, and any help would be appreciated.
>>
>> Peter T. Parrish, Ph.D.
>> President, California Solar Engineering
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address:RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200812/731829f2/attachment.htm>


More information about the RE-Wrenches mailing list