[RE-wrenches] Tesla Powerwall 2.0 - AC Coupling
Chris Sparadeo
sparadeo.chris at gmail.com
Wed Jul 22 20:14:41 EDT 2020
Max AC input is 7.6 kW AC for 10 seconds. If you are designing a system to
function off-grid you will want to size your AC input at 5kW as this is the
continuous max charge. Anything above 5kW for longer than 10 seconds and
the Powerwall will throttle back PV via frequency shift.
On Wed, Jul 22, 2020 at 3:50 PM August Goers <august at luminalt.com> wrote:
> Tesla's guidelines are 7.6 kW inverter AC rating.
>
> August
>
>
> On Wed, Jul 22, 2020 at 12:18 PM Dave Angelini Offgrid Solar <
> offgridsolar at sti.net> wrote:
>
>> Schneider uses 1.25 max on an XW for Ac coupling. That would be 1.25 x 6
>> kw or 7.5kw max from the grid inverter when ac coupling.
>>
>> I doubt your numbers would work well with a 5kw internal powerwall. Maybe
>> if you had 2 poweralls? Better get info from Tesla or the installer on
>> Wrenches. Good Luck!
>>
>>
>>
>> *Dave Angelini Offgrid Solar
>> "we go where powerlines don't"
>> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
>> e-mail offgridsolar at sti.net <offgridsolar at sti.net>
>> text 209 813 0060*
>>
>> On Wed, 22 Jul 2020 07:24:48 -0400, rich at solartechvt.com wrote:
>>
>> Considering the lack of public info available for the Powerwall, does
>> anyone have any insight into the AC coupling limits for a single Powerwall?
>>
>> For example, can we AC couple 10kw Solar Edge to a single Powerwall?
>>
>> Thanks
>>
>> Rich
>>
>>
>>
>> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
>> Behalf Of *Ray
>> *Sent:* Tuesday, July 21, 2020 8:39 PM
>> *To:* re-wrenches at lists.re-wrenches.org
>> *Subject:* Re: [RE-wrenches] Tesla Powerwall 2.0 - Experience?/Generator
>> charging
>>
>>
>>
>> That's going to be long extension cord for most off grid projects.......
>>
>> Ray Walters
>>
>> Remote Solar
>>
>> 303 505-8760
>>
>> On 7/21/20 12:11 PM, Matt Partymiller wrote:
>>
>> Jay,
>>
>>
>>
>> The Tesla Gateway has a 12v input terminal for boot up. To startup my
>> off grid Powerwall we wired in a 12V power supply to the input terminals
>> and plugged the other side into a grid-connected outlet.
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> --
Chris Sparadeo
C_802-369-4458
H_802-728-3059
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200722/492d882b/attachment.htm>
More information about the RE-Wrenches
mailing list