[RE-wrenches] Tesla Powerwall 2.0 - Experience?/Generator charging
Jason Szumlanski
jason at floridasolardesigngroup.com
Tue Jul 21 16:55:26 EDT 2020
I'm not a fan of this strategy. What happens when the coil fails? It's not
a failsafe solution IMO.
Jason Szumlanski
On Tue, Jul 21, 2020 at 10:52 AM <drake.chamberlin at redwoodalliance.org>
wrote:
> Larry,
>
> Connect the coil of a 240 VAC contactor to the output of the generator
> circuit. Have the contacts of the relay break the AC coupled feed.
>
> Drake
> ---
>
>
>
> On 2020-07-20 16:25, William Miller wrote:
>
>
>
> Larry:
>
>
>
> If you can automate disabling grid-sell when connected to the generator in
> a fool proof manner then you may have a solution. If the system fails I
> see a damaged generator but not a life-safety issue.
>
>
>
> William
>
>
>
>
>
> *From:* larry at starlightsolar.com [mailto:larry at starlightsolar.com]
> *Sent:* Monday, July 20, 2020 1:19 PM
> *To:* William Miller; RE-wrenches
> *Subject:* Re: [RE-wrenches] Tesla Powerwall 2.0 - Experience?/Generator
> charging
>
>
>
> Hi William,
>
> Thank you for your response. I was responding to the question of use off
> grid and Hiltons question about generator use. Jason said, "But Tesla is
> clear in that they do not allow a generator to interact with the Powerwall
> in any way." This is true.
>
>
>
> Powerwall uses AC coupled inverters for off grid charging. If AC from the
> micro-inverters was switched off and the generator provided the 240 Volt to
> the Powerwal inverter inputl, would that not be a temporary solution to the
> generator prohibition? The power wall would see incoming power and sync. Of
> course, the system *must* be monitored. If the power wall calls for
> cutback or disconnect by raising frequency, the generator should be
> disconnected, if it indeed works like that. If Powerwall provides an
> internal disconnect, then it would be safer for the user. Just trying to
> think outside the box.
>
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
>
>
>
> On Jul 20, 2020, at 12:01 PM, William Miller <william at millersolar.com>
> wrote:
>
> Larry:
>
> I am not Tesla conversant but allow me to speculate: If any grid-tied
> system can be fed from a generator it could also feed back to the
> generator, which may damage said generator. The grid-tied system should
> therefore be connected upstream of any transfer switching, making it
> ineligible to be charged from the generator.
>
> William
>
>
>
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
> Behalf Of larry at starlightsolar.com
> Sent: Monday, July 20, 2020 10:52 AM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Tesla Powerwall 2.0 - Experience?
>
> Since the Powerwall is AC coupled, how will it know if the power source is
> a PV solar array or a generator if either feed the PV input? It seems
> simple AC switching is all that would be needed. I like to think outside
> the box but I'm not familiar with Powerwall.
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
>
> On Jul 20, 2020, at 9:53 AM, Jason Szumlanski <
> jason at floridasolardesigngroup.com> wrote:
>
> The Powerwall 2 is now supported by Tesla in an off-grid configuration
> from what I heard. It is AC coupled. It cannot interact with generators
> whatsoever. You can't charge the battery with a generator and you can't AC
> couple a generator to it. If you want a generator, you put a transfer
> switch on the load side of the gateway device. If the battery dies,
> the generator starts. The generator powers loads, but does not recharge the
> battery because it becomes isolated via the transfer switch. The big
> downside I see with that is there would be a loss of power to the loads
> until the generator fires up. I don't see a way around that.
>
> I'm not a Tesla certified installer, but I have seen some of these
> batteries out in the wild and that's just the way it is - it's an
> integrated unit. I'd call it an "AC Battery," kind of like an AC PV Module.
> To answer another point in this thread, if the battery reaches its LBCO it
> can only recharge with PV in an off-grid scenario. It reserves battery
> capacity to turn on occasionally to see if there is PV input. At least
> that's how I understand it to work. I don't know what would happen if the
> battery actually reached 0%. Seems risky. I'm not sure how you would "jump
> start" it. Publicly available details seem scant on this, but there are a
> few system owners talking about it if you dig deep on the Interwebs.
>
> It will be interesting to see what Enphase comes up with. There are
> generator inputs on their Ensemble system, but no software support for this
> yet. The concept is very similar to Tesla in that there is a gateway
> device, essentially a transfer switch with battery controls inside. The
> Gateway acts as the AC point of coupling for everything to tie in together.
>
> I'm not sure why you couldn't use a generator to charge the Powerwall
> battery the same way you would charge with the grid. However, you would
> need a way to disable PV AC coupling when the generator is running. I can
> see how Enphase would be able to do this pretty easily. But Tesla is clear
> in that they do not allow a generator to interact with the Powerwall in any
> way.
>
> Jason Szumlanski
>
>
> On Sun, Jul 19, 2020 at 11:43 AM Hilton Dier III <hiltondier at gmail.com>
> wrote:
>
> Greetings, Wrenches,
> I have an off-grid client who has been reading the buzz about the Tesla
> Powerwall 2.0. I have been reading the data sheets and manual for it and it
> appears to be AC coupled only. There was talk of a DC input version, but
> apparently that fell by the wayside. I try to be agnostic about technology,
> and I'd be willing to subcontract a Tesla-approved installer if, in fact,
> this was the best solution.
> Does anybody have experience using the Powerwall 2.0 in an off grid PV
> system? Is it AC coupled only? Can it take generator power without barfing?
> What is the lead time on these?
> Many Thanks,
> Hilton
> --
> Hilton Dier III
> Missisquoi River Hydro
> Renewable Energy Design
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/123bef98d2c21150618c005ee1c8091cb8b371cd?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=b3ff3356e3c1e88a>
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/a1a4039218db91be6a794bdf655241b148540f5b?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=741e6df08059466a>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/1e661165431c56da3d55989ebb1b14a826eb4aa5?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=2502bdbcf570f662>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/ab2f685b0f41a8126f55dbcf37b767f81a718abf?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=40f1ca42b298d7e5>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/12858e0aa9807c3e1449eadc42b21bbc59195c54?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=16fbb28e76699ad9>
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/9924d3f6d81d5020acdca6ac8708b8cb7c8b246e?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=df88400efff41dbe>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/40089a1c4f3393f96f10b32321c5b86f1a00b23d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=5f4544a0b15d9008>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/b4516e8c36ea0ebc84a37f5972c187c2afcd4043?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=238526b124572e72>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/0a3cde5cf05bb3409566baf0805b15c790af567b?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=fd10b7f281fceb6d>
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/86feae6b5c8397245446d19fad21f00341f1f620?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=7bd9cd12839ab95e>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/a56377e13bb44dc17d699afd6ee71b0c69553132?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=bccf1980d4e6e7c6>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/f75c82f9ca1d0f53c76588132b605c452e604b52?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=be438654475f18ad>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200721/728f83c1/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 26109 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200721/728f83c1/attachment.png>
More information about the RE-Wrenches
mailing list