If its attached to the building then its subject to 690.12.  Is he also 
making you comply with rapid shutdown?

Ray Walters
Remote Solar
303 505-8760

On 7/20/20 2:01 PM, Kirk Herander wrote:
> Hey Dave,
> Well my building inspector is just being a dick about the "need" for a 
> fence surrounding the side of a wall-mount PV awning. He has 
> mis-classified it as a ground-mount per NFPA 1 rules, which requires 
> 10' clearance for ground mounts, and doesn't care about wires being 
> accessible or not. This is Burlington VT after all.
>>
>> On 7/20/2020 2:45:04 PM, palumbo131m at gmail.com 
>> <palumbo131m at gmail.com> wrote:
>>
>> Much like Sam’s but accomplished with plastic composite lattice. This 
>> pic is from 2011. The zip ties are stainless steel core.
>>
>> We operated only in Vermont where only 3 systems were inspected out 
>> of over 500 installs, this wire screening was not required. But I 
>> felt that we should be doing work up to a reasonable national safety 
>> standard, and 2 of us were NABCEP certified.
>>
>> David Palumbo
>>
>> 462 Solar Way
>>
>> Hyde Park, VT 05655
>>
>> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On 
>> Behalf Of *Sam Haraldson
>> *Sent:* Monday, July 20, 2020 1:16 PM
>> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> *Subject:* Re: [RE-wrenches] protecting wire below 8' w/awning array
>>
>> Much like Ray we have interpreted this protection to mean the 
>> "dangerous" parts of the solar and not the module frame.  As such we 
>> employed plastic "deer fence" Tek screwed to some racking components 
>> in one array where the client wished for more tamper-resistance at 
>> the point where the conductors were close to the ground.
>>
>> Another solution similar to this is employed by All Earth Renewables 
>> for their ground mount arrays that employs a tasteful looking piece 
>> of opaque coroplast.  It rests along the backside of the modules to 
>> keep people's hands from touching conductors and looks a little 
>> cleaner than a piece of mesh.
>>
>>
>>
>> 	
>>
>> *Sam Haraldson <mailto:sam at onsiteenergyinc.com>*
>>
>> 	
>>
>> Installation & Service Manager
>>
>> 	
>> 	
>> 	
>>
>> 	
>> 	
>>
>> Image removed by sender. <http://www.onsiteenergyinc.com/>
>>
>>
>>
>>
>>
>> 	
>> 	
>> 	
>> 	
>> 	
>> 	
>> 	
>> 	
>>
>>
>> Image removed by sender. <https://www.facebook.com/onsiteenergysolar/>
>>
>> 	
>> 	
>>
>> Image removed by sender. <https://www.instagram.com/onsiteenergyinc/>
>>
>> 	
>> 	
>>
>> Image removed by sender. <https://twitter.com/onsiteenergyinc>
>>
>> 	
>> 	
>>
>> Image removed by sender. 
>> <https://www.linkedin.com/company/onsite-energy-inc/>
>>
>> 	
>>
>>
>> 	
>> 	
>>
>> Image removed by sender. <https://onsiteenergyinc.com/bcorp>
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200720/6012eb89/attachment.htm>


More information about the RE-Wrenches mailing list