[RE-wrenches] SMA Sunny Storage AC-coupled with SB6.0 won't recharge LG Resu batteries during backup ops

Jerry Shafer jerrysgarage01 at gmail.com
Wed Jul 15 17:37:47 EDT 2020


Scot
We do it pretty often and have never had an issue, right out of the gate we
were told that BYD is the only battery option available, l understand your
frustration but how did you determine that LG was an approved solution in
the beginning. SMA is not perfict and I will say they do have an issue
regarding stacking of the SBS's you just can not do it, but on the PV side
it's all good.
Jerry

On Wed, Jul 15, 2020, 11:17 AM <scot.arey at solarcentex.com> wrote:

> An update.
>
>
>
> LG ESS is simply not compatible with the SMA represented system of SMA
> storage inverter, Automatic Backup Unit, and its SMA PV inverter.
>
>
>
> Just cannot AC Couple and use solar to recharge the batteries because as
> soon as the battery changes from charging to discharging, it bleeds off
> voltage in its DC to DC converter and that causes the storage inverter to
> drop…and that causes the PV inverter to drop…then it starts anew.
>
>
>
> SMA makes reference to this obliquely in it “background knowledge”
> documentation but even that asterisked verbiage doesn’t drive home the
> point that one just cannot AC couple the PV inverter to gain solar
> charging. And of course if that’s the case, why the heck would one even
> couple via a “whole house backup” SMA Automatic Backup Unit??? The answer
> if course one would not.
>
>
>
> Supposedly the BYD battery which is a true 400V battery and does not have
> the DC to DC converter does not have the same power lapses and will work in
> this architecture.
>
>
>
> Let’s see how SMA fixes this with their documentation representing this
> would all work.
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200715/40c899a5/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 37150 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200715/40c899a5/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 37150 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200715/40c899a5/attachment-0001.png>


More information about the RE-Wrenches mailing list