[RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s
Chris Schaefer
chris at solarandwindfx.com
Thu Jun 25 19:59:57 EDT 2020
Well after just a little over 2 hours on hold I did get through to a very
understanding tech support rep. I explained the issue and that the only LED
on the board that was on was the D21 (Remote Pwr). Today I learned that
this is powered by the Hub. Thus the PSB is indeed dead. I was given a
choice of either a replacement PSB or an entirely new inverter. Apparently
there has been an ongoing issue with the power supply boards lately and in
order to figure out why the engineering department would like to get the
entire unit returned for testing purposes. So for the sake of all of us out
in the field I agreed to replace the entire inverter in hopes that this
problem can be eliminated. Thanks for all your input and now we have yet
another tool in our "mental" toolbag.
Gratefully,
Christopher
On Thu, Jun 25, 2020 at 6:31 PM William Miller <william at millersolar.com>
wrote:
> Kirk:
>
>
>
> If my memory is correct: What you describe below are port assignments if
> one is stacking FXR inverters for 120/240 with a Hub 10.3. It also
> requires changing DIP jumpers from factory defaults. This is not accurate
> for stacking Radians. With Radians I think secondary inverters can use any
> port but I have always used 2 through X for secondaries.
>
>
>
> William
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Kirk Herander
> *Sent:* Thursday, June 25, 2020 2:07 PM
> *To:* re-wrenches at lists.re-wrenches.org
> *Subject:* Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @
> Mate3s
>
>
>
> The master-slave config types and port assignments have always been
> confusing. The quick start guide lists a config where the master is port 1
> and the slave is port 7. I believe port 7 is called the sub-master in this
> config. With only 2 inverters it functions as the slave to the master in
> port 1. This config has always worked for me.
>
>
>
> Hope this is accurate info.
>
> On 6/25/2020 1:35:55 PM, Chris Schaefer <chris at solarandwindfx.com> wrote:
>
> G'Day All,
>
>
>
> So I started up a system recently with two Radian 8048A's. The master is
> connected to port 1 and the slave connected to port 2 with the FlexNet at
> port 3. There are no OB charge controllers in the system. When the hub is
> polling (led's scrolling) nothing shows up for the slave at port 2. It's
> like the slave inverter doesn't exist. So I moved the slave and flexnet
> down to port 3 and 4. No change in the polling. I swapped out comm (factory
> green) cables. Again no change. Looking at the control board of the slave
> there is only one green led on which is located at the upper right-hand
> side. Otherwise no led's are on. I have 57v at the buss bar terminals of
> the inverter. Of course since there is no polling at the hub there is no
> way to view port 2 to view the slave at the Mate.
>
>
>
> Now the only thing that I didn't do was to try and use the manual on/off
> switch-jumper to start the slave. But in the past regardless of the
> inverter being on or off it would still show up on the hub. This is a new
> one and I'm looking for some direction here.
>
>
>
> Thanks,
>
> Christopher-
>
> Chris Schaefer’s
> *Error! Filename not specified.* <http://www.solarandwindfx.com>
>
> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
> *5115 South Hill Road ~ Canandaigua New York 14424www.solarandwindfx.com
> <http://www.solarandwindfx.com> ~ E-mail: **chris at solarandwindfx.com
> <chris at solarandwindfx.com>*
>
> *Error! Filename not specified.*
>
> Thomas Jefferson, the author of our great Constitution, once said,
> "democracy" will cease to exist when you take away from those who are
> willing to work and give to those who would not."
>
> _______________________________________________ List sponsored by Redwood
> Alliance List Address: RE-wrenches at lists.re-wrenches.org Change
> listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or
> update participant bios: www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
--
Chris Schaefer’s
<http:www.solarandwindfx.com>
*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
<http://www.solarandwindfx.com> ~ E-mail: chris at solarandwindfx.com
<chris at solarandwindfx.com>*
Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200625/4865f8c6/attachment.htm>
More information about the RE-Wrenches
mailing list