[RE-wrenches] Charging a Bolt with an SW
Darryl Thayer
darylsolar1 at gmail.com
Sun Jun 7 14:53:01 EDT 2020
I think you said it well, about 5 years ago I tried to charge a car from an
off-grid system. I did not record my events but the inverter had twice the
power of the level two charger, yet the inverter would get hot and trip
out. I was told a ferroresonant transformer may help, and it might be
different with different cars. However, I was warned the ferroresonant was
to stop input wave problems from arriving at the output not to prevent the
output wave problems showing up on the input. The off-grid customer gave
up.
On Sun, Jun 7, 2020 at 6:36 AM Hilton Dier III <hiltondier at gmail.com> wrote:
> The issue with EV chargers is that they create a lot of reactive power.
> Think of it as "slosh" in the waveform. That means that charging at 2,000
> watts sloshes a lot more than 2kW through the cable, plug, outlet, and from
> the inverter. If you've got a reasonably good sinewave inverter the charger
> will like it fine. However, the inverter might not like the charger if you
> cut things too close. Make sure to have a lot of top end left in your
> inverter. Always use a transformer based inverter. The SW series has a big
> chunk of metal in it, so that's good. At 120V the Bolt will only draw 1440
> watts max.
>
> An aftermarket Bolt 240V charger can draw up to 32 amps. That's 7.7 kW, so
> too big for an SW. Treat it more like 40 amps. The OEM 120/240 EVSE (smart
> charging cord) that comes with the car can draw 8 or 12 amps at 120V or 12
> at 240V. Assume that the 8 amps is really 12 and the 12 is really 15 or a
> bit more. I have seen 15 amp plugs and outlets with the hot prong melting
> plastic around it. The plug on the OEM EVSE is 20A rated but make sure your
> outlet is as well.
>
> --
> Hilton Dier III
> Missisquoi River Hydro
> Renewable Energy Design
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200607/b6b950b7/attachment.htm>
More information about the RE-Wrenches
mailing list