Bill; If it's the IFC (International Fire Code) you need to comply with,
the reference is 605.11.2 in 2012 and 2015 IFC -- Location of DC
Conductors, which states they should be located at least 10 inches below
the roof decking, and as close as possible to supporting members
(firefighters won't cut through supporting members).
If your AHJ is using IFC 2018, Location of DC Conductors was not included
in the new 1204 Energy Systems chapter, as the system should have NEC 2020
690.12 Rapid Shutdown, which makes location of DC conductors moot, as they
shouldn't be energized anyway after actuating RSS.
In cases like where there is no RSS (for example the 690.12 exemption for
non-habitable structures intended only to house PV BOS) the AHJ could
require IFC 605.11.2 compliance.
Always check with your AHJ(s) as Fire Codes are frequently amended/excepted
by local authorities.....though at least these sometimes make it into the
next IFC cycle (for example the Boulder CO and CA and OR rooftop setback
exceptions are now in IFC2018).
Dan Fink
Buckville Energy Consulting
On Fri, Jun 5, 2020, 10:46 frenergy <frenergy at psln.com> wrote:
> Hey Folks,
>
> I need some clarification, I'm getting conflicting views.
> When running DC in metal conduit from the roof array to the exterior
> wall mounted string Inverter and the attic is the way to go (for various
> reasons, usually snow), how far below the roof does that conduit have to
> be? Secured to the bottom of a rafter or top chord OK? Distance
> from???restrictions?
>
> TIA,
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
>
>
> --
> This email has been checked for viruses by Avast antivirus software.
> https://www.avast.com/antivirus
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200605/45dc91a1/attachment.htm>
More information about the RE-Wrenches
mailing list