[RE-wrenches] Enphase intermittent breaker trippjng

Jerry Shafer jerrysgarage01 at gmail.com
Mon Jun 1 13:03:14 EDT 2020


You can tighten up the graph to minutes, even seconds if you set it up to
do so
Jerry

On Mon, Jun 1, 2020, 10:01 AM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:

> I didn't think an eGauge would provide that granular of detail if there is
> a very brief intermittent issue. If I'm wrong about that it might be worth
> a try.
>
> What I really want to do is install a separate breaker in the main panel
> for the Envoy so it doesn't lose power when the IQ Combiner main breaker
> trips. I wonder if that would provide me any insight into what's happening
> immediately after the PV branch circuit and feeder circuit trip.
>
>
>
>
> On Mon, Jun 1, 2020 at 12:48 PM Jerry Shafer <jerrysgarage01 at gmail.com>
> wrote:
>
>> Jason, Wrenches
>> Can you install a data logger, say an eguage so you can see spikes or a
>> frequency shift, surge, most anything.
>> Install two non connected breakers to isolate the line, just for testing
>> purposes and see if it's only one that pops.
>> Jerry
>>
>>
>> On Mon, Jun 1, 2020, 9:11 AM Jason Szumlanski <
>> jason at floridasolardesigngroup.com> wrote:
>>
>>> I considered that, but it's tripping at night, so it's not a power
>>> output issue. It does have #6 wire, so this could be done, but I don't
>>> think it's related. It's a genuine CH240 breaker. We even replaced it once
>>> before.
>>>
>>> At this point, I must have a fault or faults on the roof. Maybe a rodent
>>> chewed through some wires. I'm going to wait for another fault and then go
>>> pull the modules to check it out.
>>>
>>>
>>>
>>> On Mon, Jun 1, 2020 at 11:00 AM jay <jay.peltz at gmail.com> wrote:
>>>
>>>> Hi Jason,
>>>>
>>>> My curiosity is about both breakers tripping.
>>>> I would suggest using a larger output breaker, I believe its a 40, put
>>>> in a 50 as a test.  I would assume the wire size will still be protected by
>>>> the 50.
>>>>
>>>> And I would also ask if the breakers are actual CH or clones?
>>>>
>>>> jay
>>>>
>>>> peltz power
>>>>
>>>> On Jun 1, 2020, at 7:23 AM, Jason Szumlanski <
>>>> jason at floridasolardesigngroup.com> wrote:
>>>>
>>>> Well, that didn't resolve it. The main breaker and a branch circuit
>>>> breaker tripped again a few days ago. It was the same branch this time.
>>>>
>>>> As my next diagnostic step I swapped two circuits (on which breaker
>>>> they are landed). If history is a guide, it will work for about two weeks
>>>> and then trip again.
>>>>
>>>> I'm dumbfounded. I really don't want to have to tear this whole system
>>>> apart. At this point, if I have to remove all the modules, I feel that I
>>>> need to replace all of the trunk cable which is an expensive proposition. I
>>>> really don't know what else to do at this point.
>>>>
>>>> Jason
>>>>
>>>>
>>>> On Mon, May 25, 2020, 10:43 AM Jason Szumlanski <
>>>> jason at floridasolardesigngroup.com> wrote:
>>>>
>>>>> I strongly suspect the CH240 combined breaker was compromised (we will
>>>>> see). Since it happened that two different strings tripped, I doubt I have
>>>>> two microinverters with internal faults. It has to be the combined breaker.
>>>>> I was just surprised that branch circuit breakers were tripping
>>>>> simultaneously with the combined output breaker.
>>>>>
>>>>> Of all the supply side connected systems I have installed, I have
>>>>> never seen a combined output fusible disconnect fuse blow, but I have seen
>>>>> many combined output breakers tripped. I was worried early on that I would
>>>>> be replacing fuses constantly, but that has not been an issue whatsoever.
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> On Thu, May 21, 2020 at 11:15 AM <scot.arey at solarcentex.com> wrote:
>>>>>
>>>>>> Actually, we had a IQ7 string loaded up to its max panel size and max
>>>>>> string length and in the spring on cool, clear day, it tripped the string’s
>>>>>> associated breaker in the Enphase combiner.
>>>>>>
>>>>>>
>>>>>>
>>>>>> We reset but of course that breaker was impaired and it tripped
>>>>>> again. We replaced and never had an issue going forward. We suspect the
>>>>>> breaker was less than perfect from the start as we’ve add equally nice days
>>>>>> since.
>>>>>>
>>>>>>
>>>>>>
>>>>>> This almost reminds me of loading up Outback FM80. It says 4,000
>>>>>> watts but in reality, 3,600 is the max when amps spike. I will be extra
>>>>>> careful going forward on IQ7 string length when going to the max published…
>>>>>>
>>>>>>
>>>>>>
>>>>>> My story.
>>>>>>
>>>>>>
>>>>>>
>>>>>> Scot
>>>>>>
>>>>>>
>>>>>>
>>>>>> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
>>>>>> Behalf Of *Jason Szumlanski
>>>>>> *Sent:* Thursday, May 21, 2020 8:57 AM
>>>>>> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
>>>>>> *Subject:* [RE-wrenches] Enphase intermittent breaker trippjng
>>>>>>
>>>>>>
>>>>>>
>>>>>> I'm trying to resolve an intermittent frustrating problem with and
>>>>>> Enphase IQ system. There are three AC Branch circuits of 9 microinverters
>>>>>> each coming into an Enphase AC combiner.
>>>>>>
>>>>>>
>>>>>>
>>>>>> What has been happening is one of the BR220 branch circuit breakers
>>>>>> and the combine CH240 breaker in the main backfed load center have been
>>>>>> tripping simultaneously. It has happened about four times in the last 6
>>>>>> months. It was always the same branch circuit breaker, so we kept
>>>>>> investigating that string, checking the junction box, trunk cable, and cap,
>>>>>> etc. Finally we swapped out the BR220 breaker.
>>>>>>
>>>>>>
>>>>>>
>>>>>> Fast forward 4 weeks, and we got another call. This time a different
>>>>>> branch circuit breaker and the main breaker tripped simultaneously. We
>>>>>> checked that branch circuit and could not find any fault. It seems unlikely
>>>>>> that two branch circuit breakers would be faulty, so we have now switched
>>>>>> out the CH240 main breaker in hopes that it is the culprit.
>>>>>>
>>>>>>
>>>>>>
>>>>>> I'm not totally confident in this resolution and I have my fingers
>>>>>> crossed. If that doesn't work, does anyone have any suggestions on another
>>>>>> diagnostic step? These intermittent problems are a major hassle. One
>>>>>> thought I had was to switch to a supply side interconnection with a fusible
>>>>>> disconnect. Maybe the intermittent fault would blow one of the two line
>>>>>> fuses so at least I could narrow it down to which line the fault is on if
>>>>>> there is in fact a fault.
>>>>>>
>>>>>>
>>>>>>
>>>>>> I have experienced two other tripping breaker issues with Enphase
>>>>>> systems in the past. Neither of them were systems I installed. One turned
>>>>>> out to be branch circuits that were not properly paired up and landed on
>>>>>> different breakers. Another time we had an inverter with an internal fault
>>>>>> which eventually"blew up" with a loud popping noise and smoke billowing out
>>>>>> of it. That happened after resetting a trip breaker multiple times. This
>>>>>> case seems to be unrelated to those issues. I'm perplexed.
>>>>>>
>>>>>>
>>>>>>
>>>>>> Jason Szumlanski
>>>>>>
>>>>>> Florida Solar Design Group
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>>
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/597d17191a5e04849606ae0978333668b3700063?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=7436ab18d052ff54>
>>>>>>
>>>>>> List-Archive:
>>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>> <https://mailtrack.io/trace/link/be955f33c15547578a4fc2bb22bf238522aa477e?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=9be69f034134d9b4>
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> www.re-wrenches.org/etiquette.htm
>>>>>> <https://mailtrack.io/trace/link/37d4383fa02be169603fef8dbe360c863c710439?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=63e51273639b9542>
>>>>>>
>>>>>> Check out or update participant bios:
>>>>>> www.members.re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/b643dd0abd9eb4a8d196ec139cd09e572d06e6f9?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=0430680b3b6e2d61>
>>>>>>
>>>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> <https://mailtrack.io/trace/link/df0e2e59561d3b11496653cc85f74e7b7cdab5c9?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=31445c3aaaefd3c8>
>>>>
>>>> List-Archive:
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>> <https://mailtrack.io/trace/link/2d93803e6c8582b3660cdd325929fa4482ac4984?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=22684b51e4b9da02>
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> <https://mailtrack.io/trace/link/54455909957ff19dd90a81cd722af627b419a8d7?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=8d047bdd00a9d6ed>
>>>>
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> <https://mailtrack.io/trace/link/6107c11ffabf5a4025fcaf1100651df4f6aa71a1?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=6167ff65093dd260>
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> <https://mailtrack.io/trace/link/15219f6d22eeb416c669cb55f284b629c5c2cbe7?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=90e649247565e91b>
>>>>
>>>> List-Archive:
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>> <https://mailtrack.io/trace/link/04596f882cd6d16465520d534c4d59c99c491494?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=2cb17b68a275b287>
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> <https://mailtrack.io/trace/link/d1879e411303f7b0103006c8a53edd6025dcd399?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=2a4945ad2e3d9186>
>>>>
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> <https://mailtrack.io/trace/link/74f6a3449a21a935bedb9d2235fe7a0cfae9ed94?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=50b803bf07482633>
>>>>
>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/97767e3e244cc8b7d37ab49e038ba71838163164?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=3804c293104efd68>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> <https://mailtrack.io/trace/link/fcbc2565a7b02a30a52959e3b69c043ce4ccf9b8?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=266bc55665d31809>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/5abd1dc7f71c668c3dd3134d9b4a0363fdd44b6a?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=86bfbde8f86d546a>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/6a976b015d0a93dbfbb1b8fe732f607dcc85040d?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=b065db52a3fe28d4>
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/1831bf37425642ff0899a292ea0584da39747b89?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=a3177329cfd397f9>
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> <https://mailtrack.io/trace/link/feff310ca96cfc1672e6e7d5ced3cfa368a9c7b0?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=cb911b0a51d3e0da>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/3ed5b7412092e46573cbe8e90ee494a092ad5622?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=e429b227807e90a6>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/4bb5e14c97b2061e8a59d8b629c18b0b8daa2e67?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=9ba46505b055f37f>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200601/f307c2d7/attachment.htm>


More information about the RE-Wrenches mailing list