[RE-wrenches] Enphase intermittent breaker trippjng
Jason Szumlanski
jason at floridasolardesigngroup.com
Mon May 25 10:43:43 EDT 2020
I strongly suspect the CH240 combined breaker was compromised (we will
see). Since it happened that two different strings tripped, I doubt I have
two microinverters with internal faults. It has to be the combined breaker.
I was just surprised that branch circuit breakers were tripping
simultaneously with the combined output breaker.
Of all the supply side connected systems I have installed, I have never
seen a combined output fusible disconnect fuse blow, but I have seen many
combined output breakers tripped. I was worried early on that I would be
replacing fuses constantly, but that has not been an issue whatsoever.
On Thu, May 21, 2020 at 11:15 AM <scot.arey at solarcentex.com> wrote:
> Actually, we had a IQ7 string loaded up to its max panel size and max
> string length and in the spring on cool, clear day, it tripped the string’s
> associated breaker in the Enphase combiner.
>
>
>
> We reset but of course that breaker was impaired and it tripped again. We
> replaced and never had an issue going forward. We suspect the breaker was
> less than perfect from the start as we’ve add equally nice days since.
>
>
>
> This almost reminds me of loading up Outback FM80. It says 4,000 watts but
> in reality, 3,600 is the max when amps spike. I will be extra careful going
> forward on IQ7 string length when going to the max published…
>
>
>
> My story.
>
>
>
> Scot
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Jason Szumlanski
> *Sent:* Thursday, May 21, 2020 8:57 AM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* [RE-wrenches] Enphase intermittent breaker trippjng
>
>
>
> I'm trying to resolve an intermittent frustrating problem with and Enphase
> IQ system. There are three AC Branch circuits of 9 microinverters each
> coming into an Enphase AC combiner.
>
>
>
> What has been happening is one of the BR220 branch circuit breakers and
> the combine CH240 breaker in the main backfed load center have been
> tripping simultaneously. It has happened about four times in the last 6
> months. It was always the same branch circuit breaker, so we kept
> investigating that string, checking the junction box, trunk cable, and cap,
> etc. Finally we swapped out the BR220 breaker.
>
>
>
> Fast forward 4 weeks, and we got another call. This time a different
> branch circuit breaker and the main breaker tripped simultaneously. We
> checked that branch circuit and could not find any fault. It seems unlikely
> that two branch circuit breakers would be faulty, so we have now switched
> out the CH240 main breaker in hopes that it is the culprit.
>
>
>
> I'm not totally confident in this resolution and I have my fingers
> crossed. If that doesn't work, does anyone have any suggestions on another
> diagnostic step? These intermittent problems are a major hassle. One
> thought I had was to switch to a supply side interconnection with a fusible
> disconnect. Maybe the intermittent fault would blow one of the two line
> fuses so at least I could narrow it down to which line the fault is on if
> there is in fact a fault.
>
>
>
> I have experienced two other tripping breaker issues with Enphase systems
> in the past. Neither of them were systems I installed. One turned out to be
> branch circuits that were not properly paired up and landed on different
> breakers. Another time we had an inverter with an internal fault which
> eventually"blew up" with a loud popping noise and smoke billowing out of
> it. That happened after resetting a trip breaker multiple times. This case
> seems to be unrelated to those issues. I'm perplexed.
>
>
>
> Jason Szumlanski
>
> Florida Solar Design Group
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/796b1796eb4c075a74298513a530f62e4a496cb2?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c7dea131fd9cb45a>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://mailtrack.io/trace/link/c06e48af2da3d129a58c08ef2043bd2d8fcbef6f?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=06899a19621f54d8>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/215cb4d0fcfb04e4124aae9b2616249f1eef5542?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=8bc84049c81c183c>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/27c3e706e7f2b4836b1669b31c9454db7fee1b52?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=4a75a2d55681f39a>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200525/85eb4d21/attachment.htm>
More information about the RE-Wrenches
mailing list