[RE-wrenches] How much Li battery?

Darryl Thayer darylsolar1 at gmail.com
Sun May 24 16:31:51 EDT 2020


I have spoken with a li battery
researcher. Do not charge over 85% of battery full charge voltage and they
will last over 25 years.   But go above or below bottom and trouble

On Sun, May 24, 2020, 10:27 AM Jay <jay.peltz at gmail.com> wrote:

> One question I have for those more versed than me in lithium is, I’m under
> the impression that having a lithium battery in float for years isn’t good
> for it. Or at the very least it has to be cycled with some regularity.
>
> I’d like to hear data on that
>
> Thx
> Jay
>
> Peltz power.
>
>
>
>
>
> On May 23, 2020, at 10:08 PM, Ray <ray at solarray.com> wrote:
>
> 
>
> I suggest starting with a very simple look at the continuous output rating
> of the battery and match that to the inverter continuous rating. This ends
> up with quite a bit more battery than you might think at first.  However,
> if the customer paid the big bucks for a battery backup system, they should
> at least get enough battery to operate the inverter at its rated power.
> Anything less, I would consider poor design.  The same goes for lead acid
> batteries, they just don't work well, even on grid, when the battery is
> undersized.  Even lead acid batteries have maximum current output ratings
> that should at least be matched to the inverter rating.
>
> If you WERE going to under size the battery, then you should keep it safe
> by reducing the size of the inverter battery breaker as well.   I know this
> "micro battery for GTB" is becoming a trend, but it doesn't mean its right.
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 5/23/20 5:48 PM, Mick Abraham wrote:
>
> Greetings, All~ Mark Frye had asked:  "...with a 4000w Outback Radian, AC
> coupled with 2000w of PV, what is the smallest Li battery I would want for
> stable operation?"
>
> Mick's reply: In the lithium arena, one often finds the ratings in
> kilowatt-hours rather than in amp-hours. This is an easy conversion for us
> energy nerds to make, so below I'm mainly using watts & watt-hours with
> occasional conversions to amp-hours.
>
> I suggest that you start with the spec sheet (of whichever brand lithium
> battery is on your radar), & see what the manufacturer says about
> "allowable rate of recharge". You may find that C/2 is an acceptable rate
> with several manufacturers, Mark--much faster than what we're accustomed to
> with typical lead-acid batteries. Let's assume:
>
> * ...that your AC coupled PV array crests around 1800 watts to the battery
> when there are no loads
> * ...that the battery is below 100% state of charge, and
> * ...that the solar conditions are optimal.
>
> Let's further assume that those conditions represent your battery's
> highest energy rate in either direction.
>
> 1800w X two hours = 3,600 watt-hours dividing by 48v nominal = 75
> amp-hours in the above hypothetical situation.
>
> ++++++++++++++++++++++++++++++
>
> The rate at which a battery can receive energy is (usually) also the rate
> at which it can comfortably deplete, so let's briefly look at the flip
> side: Assuming the battery mfr. wants the watt-hours to be no less than two
> times the maximum wattage, a 3600 watt-hour (C/2) battery should not be
> depleted faster than 1800 watts. Your 4kW Radian, Mark, could exceed that
> if the loads demand it--& maybe your loads don't. Motor starting surges
> should probably be part of the thinking & it wouldn't hurt to ask the
> mfr.'s opinion about short term surges which briefly deplete the battery
> faster than the hypothetical two hour rate.
>
> By approaching this question based on the battery manufacturer do's &
> don'ts, one improves the chance of getting warranty coverage should it
> later be needed. "What the large print giveth, the fine print taketh away."
>
> The Wrench List is the Bomb!
>
> Mick Abraham, Proprietor
> www.abrahamsolar.com
>
> Landline: 970-731-4675
> Cell phone or for text messaging: 970-946-6584
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200524/a0c4c389/attachment.htm>


More information about the RE-Wrenches mailing list