[RE-wrenches] Outback EQ not holding voltage

Dave Tedeyan dtedeyan at taitem.com
Tue Apr 28 12:20:26 EDT 2020


Steve and Jerry,
Thanks for the suggestions. I'll have to take a closer look at the battery
bank next time I am out there.
The solar setup is 4 strings of 3 kyocera 270's into each charge
controller. So that is almost 65A @50V coming out of each charge controller
for bulk. The parallel battery strings all have the same length of premade
cable, so current should be balanced (unless there is a dead cell or two in
there...).
Cheers,
Dave

*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC

110 South Albany Street | Ithaca, NY 14850
o. *607.277.1118 x121*  f. 607.277.2119
www.taitem.com

Solar • Sustainability • Energy • Design
Certified B-Corporation since 2013


On Tue, Apr 28, 2020 at 11:52 AM Jerry Shafer <jerrysgarage01 at gmail.com>
wrote:

> Sounds like a battery issue at first glance, as you EQ a battery it gets
> warm or even hot and this will effect ability to charge. If e en one of the
> L-16 is not exactly the same voltage you will not get to EQ untill another
> battery over voltages to show your overall volts. Need to look at each
> battery volts under this charge condition. Also if you have a battery
> acting up be very careful working around them.
> Jerry
>
> On Tue, Apr 28, 2020, 6:50 AM Dave Tedeyan <dtedeyan at taitem.com> wrote:
>
>> Hi All,
>>
>> I've got an outback system (Radian 8048A, 2 FM80, 16 Trojan L16RE-B)
>> where when the customer equalizes, the batteries hover right around the EQ
>> voltage, but will often dip to 0.1v less. Because of this, the EQ timer
>> does not count down properly, and so left to its own devices the system
>> would equalize for way longer than it should, potentially forever. This
>> will happen when doing an EQ from the solar on a bright sunny day, or the
>> generator, or both. The customer can manually keep track of the time and
>> manually stop the EQ after 3 hours, but that is not ideal. Has anyone dealt
>> with this before and have any suggestions on how they fixed it?
>>
>> This system is 3-4 years old, and the issue only started in the past year
>> or so.
>>
>> Cheers,
>> Dave
>>
>> *Dave Tedeyan, PE*
>> Senior Engineer | Taitem Engineering, PC
>>
>> 110 South Albany Street | Ithaca, NY 14850
>> o. *607.277.1118 x121*  f. 607.277.2119
>> www.taitem.com
>>
>> Solar • Sustainability • Energy • Design
>> Certified B-Corporation since 2013
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200428/193aeb55/attachment.htm>


More information about the RE-Wrenches mailing list