[RE-wrenches] Outback EQ not holding voltage

Brian Mehalic brian at solarenergy.org
Tue Apr 28 10:00:21 EDT 2020


Sorry you had already answered the first two questions :) What about the others?

Brian

> On Apr 28, 2020, at 6:50 AM, Dave Tedeyan <dtedeyan at taitem.com> wrote:
> 
> 
> Hi All, 
> 
> I've got an outback system (Radian 8048A, 2 FM80, 16 Trojan L16RE-B) where when the customer equalizes, the batteries hover right around the EQ voltage, but will often dip to 0.1v less. Because of this, the EQ timer does not count down properly, and so left to its own devices the system would equalize for way longer than it should, potentially forever. This will happen when doing an EQ from the solar on a bright sunny day, or the generator, or both. The customer can manually keep track of the time and manually stop the EQ after 3 hours, but that is not ideal. Has anyone dealt with this before and have any suggestions on how they fixed it? 
> 
> This system is 3-4 years old, and the issue only started in the past year or so.
> 
> Cheers, 
> Dave
> 
> Dave Tedeyan, PE
> Senior Engineer | Taitem Engineering, PC
> 
> 110 South Albany Street | Ithaca, NY 14850
> o. 607.277.1118 x121  f. 607.277.2119
> www.taitem.com
> 
> Solar • Sustainability • Energy • Design
> Certified B-Corporation since 2013
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200428/67fa130c/attachment.htm>


More information about the RE-Wrenches mailing list