Have you shortened the transfer time from gen to inv, voltage “cut out"acceptance of the gen in power instead of their 90Vac to say 110V/L ? Raising the output voltage on the 6848s & gen set for VD/voltage sag issues under heavy loading? Watch this as sometimes under heavy loading it will cut the AC input. I use the config tool to address this kind of issue, gives me a bit more control.
I have a client that has a large external battery charger similar to a fork truck unit that he alleges causes "dirty power" while the genset is supplying power to the charger, w/o charging thru the inverters. Unfortunately w/ the virus I have yet to confirm.
> On Apr 21, 2020, at 8:27 AM, Jason Szumlanski <jason at floridasolardesigngroup.com> wrote:
>
> I actually need 400Adc at 51V nominal of total charge rate. I was hoping to use 100Adc chargers for redundancy, or some combination of 2-8 chargers to reach the needed current, assuming they can be synced up. I don't think the charging algorithm needs to be complicated. We are basically bulk charging the LiPOs to 80% with the battery BMS controlling the generator. The concept is to get to 80% sometime in the night and solar kicks in during the day to reach 100% using 2-stage charging from the XW charge controllers.
>
> The problem I have is the quad XW6048s in the system run at a pretty good load typically... often over 50%. This is off-grid with generator backup. The transfer switches in the XW6048 are causing surges and brownouts when the switched loads are high, especially smart dimmers and televisions. I need seamless power for this client. My thought is to abandon the internal chargers in the XW6048s and just run loads off inverter power full-time. I would charge the batteries with external battery chargers. The tricky part is how to adjust the charge rate based on load, and also based on solar input. I need to limit the net charging current. Of course, I still need 400Adc of charging current, which I'm learning might be hard to find. I don't really want to buy four more XWs - that's a pretty expensive solution.
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
> On Fri, Apr 17, 2020 at 4:26 PM Dave Angelini Offgrid Solar <offgridsolar at sti.net <mailto:offgridsolar at sti.net>> wrote:
> I use the CSW 4048. It has a 50 amp charger. A good spare for clients. Get 2 of them. Repurpose an old Radian or XW well over 100A. XW+ is 140adc.
>
> Dave Angelini Offgrid Solar
>
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ <https://mailtrack.io/trace/link/818d0fc14d35240172dc7b5e76e9b358639d0699?url=http%3A%2F%2Fmembers.sti.net%2Foffgridsolar%2F&userId=1613865&signature=a20ca8855bc640ef>
> e-mail offgridsolar at sti.net <mailto:offgridsolar at sti.net>
> text 209 813 0060
> On Fri, 17 Apr 2020 14:21:14 -0400, Jason Szumlanski <jason at floridasolardesigngroup.com <mailto:jason at floridasolardesigngroup.com>> wrote:
>
>> I'm looking for a standalone 51V nominal battery charger suitable for a LiPO battery with 2-stage charging and adjustable setpoints for max current and battery voltage. It would require dual chargers with 100A capacity (I want dual chargers for redundancy so I have at least 50% capacity if one goes bad). Ideally they would sync up so they change stages simultaneously, but I'm not sure if that's really important.
>>
>> Who makes something like that?
>>
>> Jason Szumlanski
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <https://mailtrack.io/trace/link/47d978507b9775cf89c2c4ac9665997e7f3c2d10?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=61d5cd552bcb7a04>
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <https://mailtrack.io/trace/link/751a499f55945df4070b9d5521e2cdfbcea242a8?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=8afbf050d5afe9e0>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <https://mailtrack.io/trace/link/371ce356d356262bb1fe8e503601758f8bac958e?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=eb4588d3c5c730cd>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <https://mailtrack.io/trace/link/e9ea24bb0cec5ce64b3012496a3a8b6390d7a863?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=b340c2774b3cc0f9>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> Tump at swnl.net <blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net> www.SWNL.net <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
> Solarwinds Northernlights
> Serving Mid Coast Maine & Northern California
> 207-832-7574 Cl. 610-517-8401
> Blair "TUMP" May
> ******** MAINE'S CHARTER ********
> NABCEP "Certified PV Installer"
>