[RE-wrenches] Lithium Ion Batteries
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Mon Mar 23 11:36:45 EDT 2020
Another way to buy more time with simplyphi would be to minimize LBCO
hysteresis voltage and LBCO delay time. This would shut down the inverter
sooner. They appear to be set at the defaults and could go lower.
Dave
Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridsolar at sti.net
[2]
text 209 813 0060
On Mon, 23 Mar 2020 15:06:10 +0000, Sandra Herrera
wrote:
Hi Ray,
We have been working with most of the leading
lithium manufacturers for several years now. Some have already implemented
closed-loop integration such as Discover, other we are working with
open-loop integration with Simpliphi, Fortress, Blue Ion, others.
For the
manufactures that are open loop, we have done extensive work with them,
which included lab testing as well as support with the documentation.
I
have personally supported most of the manufacturers listed above; this
includes Simpliphi and support of their documentation, related to the
Schneider Electric setting.
With the Conext XW Pro we are moving to SOC
for many of these settings, that will integrate better than using voltage.
Additional work of integrating these manufactures using Gateway through
Modbus communication.
I know that at times it seems very simple to make a
programming change, but we as the manufacturers must look at the full
picture of all the applications of the product and not create a conflict.
An alternative would be a Simpliphi specifically firmware, this sounds very
simple, but it is cost-prohibitive, as the product would have to be UL
tested again. Each time we have to run a product through UL it will add to
the cost of the product. It is a balance between the feature and staying
competitive.
I hope this help to cl;arify, let me know if you have any
question
Sandra Herrera
Sandra.herrera at se.com
FROM: RE-wrenches ON
BEHALF OF Ray
SENT: Saturday, March 21, 2020 8:46 AM
TO:
re-wrenches at lists.re-wrenches.org
SUBJECT: Re: [RE-wrenches] Lithium Ion
Batteries
[External email: Use caution with links and attachments]
-------------------------
We've been having good luck with SImpliphi, the
pricing has recently gotten much more competitive. As it's names states,
its simple. Each 3.8 kWh unit has an 80 amp breaker built into the top,
weigh about 75 lbs, and are a bit smaller than an L16 but with carry
handles. We use an insulated 2 pole combiner block to run all the parallel
conductors to the main 2/0 cable. No monitoring, but they do have an handy
setup guide with recommended settings, specific for each manufacturer
(including Outback).
Note to all: Schneider XW can still not set its LVD
above 48, which basically makes it incompatible with most Li+ batteries.
Their tech support has been abysmal as well. We're looking forward to them
as one of the larger companies in the business, to put additional resources
into their engineering, and come out with at least a firmware update to
correct this problem.
Ray Walters
Remote Solar
303 505-8760
On 3/20/20
3:59 PM, David Katz wrote:
Hello Wrenches,
I am working with some
people that want to use a 20 kw-hour to 30 kw-hour 48 volt lithium-ion
battery with an Outback Radian and Outback FM charge controllers.
They
are considering using Discover, Blue-Ion, Battle Born or SimpliPhi
batteries.
Does any one have any recommendations of which battery
functions best with the Outback system.
Thanks,
David Katz
_______________________________________________
List sponsored by
Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
[3]
Change listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[4]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[5]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [6]
Check
out or update participant bios:
www.members.re-wrenches.org [7]
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
Links:
------
[1] http://members.sti.net/offgridsolar/
[2]
mailto:offgridsolar at sti.net
[3]
mailto:RE-wrenches at lists.re-wrenches.org
[4]
https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&data=02%7C01%7Csandra.herrera%40se.com%7C407f988227f34589ec2108d7cdaf0650%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637204023926837446&sdata=mVLv8GIMSCiqeHDJtA8m%2FJg%2FwMERGJwbjx7lP7lhGOE%3D&reserved=0
[5]
https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&data=02%7C01%7Csandra.herrera%40se.com%7C407f988227f34589ec2108d7cdaf0650%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637204023926837446&sdata=t5SwVj95dd%2FXO1GtUfhzABAHwdEX8pSWjczoKyJ%2FmQY%3D&reserved=0
[6]
https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&data=02%7C01%7Csandra.herrera%40se.com%7C407f988227f34589ec2108d7cdaf0650%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637204023926847400&sdata=4Zt7UImDoQUWI5bkd19tkzt8YMEqxqSqlRvF5kSabBY%3D&reserved=0
[7]
https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&data=02%7C01%7Csandra.herrera%40se.com%7C407f988227f34589ec2108d7cdaf0650%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637204023926847400&sdata=DF%2F6xHm6WSaXde36TVsfCsqU2h8Yu8wot2MNz49D93k%3D&reserved=0
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200323/6d87e3e2/attachment.htm>
More information about the RE-Wrenches
mailing list