[RE-wrenches] Lithium Ion Batteries

Kent Osterberg kent at coveoregon.com
Sun Mar 22 20:37:15 EDT 2020


Jay,

Do you mean: use the Aux relay to activate the Remote Power Off? What is 
the low battery setting range for the Aux relay? I don't see it in the 
manual.

Kent Osterberg
Blue Mountain Solar


On 3/22/2020 4:04 PM, Jay wrote:
> Ray,
> Have you heard bought about using the Aux relay to control the AC 
> output at what ever voltage you want?
>
> Jay
>
>
>
>
>> On Mar 22, 2020, at 3:13 PM, Ray <ray at solarray.com> wrote:
>>
>> 
>>
>> That's the whole point: we need the LBCO to be higher than 48v to 
>> catch the beginning of that steep drop off, so that there is still 
>> enough reserve left to keep the monitoring and solar charge 
>> controllers in operation, and avoid the dreaded dark start.  With 
>> Simpliphi, we don't have the dark start, but it still requires manual 
>> reset.   This isn't theoretical, we have been having serious trouble 
>> with a system because of Schneider's inability to set the LVD above 
>> 48 v.  Also setting the voltage higher (lower DOD) extends the cycle 
>> life of these batteries.  Otherwise, I love the stable 51 volts of 
>> Li+, even under load.
>>
>> Ray Walters
>> Remote Solar
>> 303 505-8760
>> On 3/22/20 4:15 PM, Jerry Shafer wrote:
>>> Wrenches
>>> Don't let the LBCU scare you as this battery has such a flat SOC 
>>> line that when it falls off there is not much left in the tank. In 
>>> addition set the flex net to low SOC at 15% and critical to 10%.
>>>
>>> On Sun, Mar 22, 2020, 12:15 PM Sindelar Solar 
>>> <Allan at sindelarsolar.com <mailto:Allan at sindelarsolar.com>> wrote:
>>>
>>>     Specifically with Blue Ion, the installation manual recommends
>>>     48V as LBCO, but also recommends setting it a bit higher:
>>>
>>>     "Recommended Low Voltage Disconnect Setting: 48 VDC (~2-10%
>>>     State of Charge)
>>>     BMU will power down the Blue Ion 2.0 cabinet at 44 VDC (<1%
>>>     State of Charge)
>>>     Based on system discharge patterns, SoC and voltage correlations
>>>     will vary.
>>>     We recommend you err on the side of caution with a higher LVD
>>>     setting and adjust as necessary.
>>>     To prevent a dark start event, we recommend leaving a little
>>>     reserve “fuel in the tank”."
>>>
>>>     I have used 48VDC with success, and had one system indeed shut
>>>     down at 44V, leaving 1% left to reboot.
>>>
>>>     Allan
>>>
>>>     On 3/22/2020 12:44 PM, Ray wrote:
>>>>
>>>>     Blue Ion, and Simpliphi that I know of.
>>>>
>>>>     Ray Walters
>>>>     Remote Solar
>>>>     303 505-8760
>>>>     On 3/21/20 2:48 PM, Dave Angelini Offgrid Solar wrote:
>>>>>
>>>>>     I see what you mean Ray. Sorry I misread your mail. There are
>>>>>     not too many batteries out there that need LBCO above 48V.
>>>>>     Which ones are you talking about please?
>>>>>
>>>>>     *Dave Angelini Offgrid Solar*
>>>>>
>>>>>     *"we go where powerlines don't"
>>>>>     http://members.sti.net/offgridsolar/ e-mail
>>>>>     offgridsolar at sti.net <mailto:offgridsolar at sti.net> text 209
>>>>>     813 0060*
>>>>>
>>>>>     On Sat, 21 Mar 2020 11:18:21 -0700, Dave Angelini Offgrid
>>>>>     Solar <offgridsolar at sti.net> <mailto:offgridsolar at sti.net> wrote:
>>>>>
>>>>>>     Hi Ray,
>>>>>>
>>>>>>     Which XW? There are 3 now. The old graybox XW defaults at 44V
>>>>>>     LBCO and the range is 40 to 48V. There also was firmware back
>>>>>>     in its day that got older units updated. Schneider still has
>>>>>>     the firmware under discontinued products.
>>>>>>
>>>>>>     XW+ is default 44V and adjustable 36 to 44 vdc.
>>>>>>
>>>>>>     XW pro is running downstairs and I will take a look. It would
>>>>>>     be my guess that it is the same as XW+. I think one needs to
>>>>>>     be sure they are in Advanced settings to tweak LBCO also.
>>>>>>
>>>>>>     I am not plugging Schneider and have done work for both
>>>>>>     Outback and Schneider as well as my clients. Hope this helps.
>>>>>>
>>>>>>     *Dave Angelini Offgrid Solar "we go where powerlines don't"
>>>>>>     http://members.sti.net/offgridsolar/ e-mail
>>>>>>     offgridsolar at sti.net <mailto:offgridsolar at sti.net> text 209
>>>>>>     813 0060*
>>>>>>
>>>>>>     On Sat, 21 Mar 2020 11:46:21 -0400, Ray <ray at solarray.com>
>>>>>>     <mailto:ray at solarray.com> wrote:
>>>>>>
>>>>>>         We've been having good luck with SImpliphi, the pricing
>>>>>>         has recently gotten much more competitive.  As it's names
>>>>>>         states, its simple.  Each 3.8 kWh unit has an 80 amp
>>>>>>         breaker built into the top, weigh about 75 lbs, and are a
>>>>>>         bit smaller than an L16 but with carry handles.  We use
>>>>>>         an insulated 2 pole combiner block to run all the
>>>>>>         parallel conductors to the main 2/0 cable.  No
>>>>>>         monitoring, but they do have an handy setup guide with
>>>>>>         recommended settings, specific for each manufacturer
>>>>>>         (including Outback).
>>>>>>
>>>>>>         Note to all:  Schneider XW can still not set its LVD
>>>>>>         above 48, which basically makes it incompatible with most
>>>>>>         Li+ batteries. Their tech support has been abysmal as
>>>>>>         well.   We're looking forward to them as one of the
>>>>>>         larger companies in the business, to put additional
>>>>>>         resources into their engineering, and come out with at
>>>>>>         least a firmware update to correct this problem.
>>>>>>
>>>>>>         Ray Walters
>>>>>>         Remote Solar
>>>>>>         303 505-8760
>>>>>>
>>>>>>         On 3/20/20 3:59 PM, David Katz wrote:
>>>>>>
>>>>>>             Hello Wrenches,
>>>>>>             I am working with some people that want to use a 20
>>>>>>             kw-hour to 30 kw-hour 48 volt lithium-ion battery
>>>>>>             with an Outback Radian and Outback FM charge controllers.
>>>>>>             They are considering using Discover, Blue-Ion, Battle
>>>>>>             Born or SimpliPhi batteries.
>>>>>>             Does any one have any recommendations of which
>>>>>>             battery functions best with the Outback system.
>>>>>>             Thanks,
>>>>>>             David Katz
>>>>>>
>>>>>>             _______________________________________________
>>>>>>             List sponsored by Redwood Alliance
>>>>>>
>>>>>>             List Address:RE-wrenches at lists.re-wrenches.org  <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>
>>>>>>             Change listserver email address & settings:
>>>>>>             http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>
>>>>>>             List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>>
>>>>>>             List rules & etiquette:
>>>>>>             www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>>>>>>
>>>>>>             Check out or update participant bios:
>>>>>>             www.members.re-wrenches.org  <http://www.members.re-wrenches.org>
>>>>>>
>>>>>
>>>>>     _______________________________________________
>>>>>     List sponsored by Redwood Alliance
>>>>>
>>>>>     List Address:RE-wrenches at lists.re-wrenches.org  <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>
>>>>>     Change listserver email address & settings:
>>>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>
>>>>>     List rules & etiquette:
>>>>>     www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>>>>>
>>>>>     Check out or update participant bios:
>>>>>     www.members.re-wrenches.org  <http://www.members.re-wrenches.org>
>>>>>
>>>>
>>>>     _______________________________________________
>>>>     List sponsored by Redwood Alliance
>>>>
>>>>     List Address:RE-wrenches at lists.re-wrenches.org  <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>
>>>>     Change listserver email address & settings:
>>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>
>>>>     List rules & etiquette:
>>>>     www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>>>>
>>>>     Check out or update participant bios:
>>>>     www.members.re-wrenches.org  <http://www.members.re-wrenches.org>
>>>>
>>>     -- 
>>>
>>>     *Allan Sindelar*
>>>     allan at sindelarsolar.com <mailto:allan at sindelarsolar.com>
>>>     NABCEP Certified PV Installation Professional
>>>     New Mexico EE98J Journeyman Electrician
>>>     Founder (Retired), Positive Energy, Inc.
>>>     *505 780-2738 cell*
>>>
>>>     _______________________________________________
>>>     List sponsored by Redwood Alliance
>>>
>>>     List Address: RE-wrenches at lists.re-wrenches.org
>>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>     Change listserver email address & settings:
>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>     List-Archive:
>>>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>     List rules & etiquette:
>>>     www.re-wrenches.org/etiquette.htm
>>>     <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>     Check out or update participant bios:
>>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200322/1a4df31b/attachment.htm>


More information about the RE-Wrenches mailing list