[RE-wrenches] Lithium Ion Batteries
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Sat Mar 21 14:18:21 EDT 2020
Hi Ray,
Which XW? There are 3 now. The old graybox XW defaults at 44V
LBCO and the range is 40 to 48V. There also was firmware back in its day
that got older units updated. Schneider still has the firmware under
discontinued products.
XW+ is default 44V and adjustable 36 to 44 vdc.
XW pro is running downstairs and I will take a look. It would be my guess
that it is the same as XW+. I think one needs to be sure they are in
Advanced settings to tweak LBCO also.
I am not plugging Schneider and
have done work for both Outback and Schneider as well as my clients. Hope
this helps.
Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridsolar at sti.net
[2]
text 209 813 0060
On Sat, 21 Mar 2020 11:46:21 -0400, Ray wrote:
We've been having good luck with SImpliphi, the pricing has recently
gotten much more competitive. As it's names states, its simple. Each 3.8
kWh unit has an 80 amp breaker built into the top, weigh about 75 lbs, and
are a bit smaller than an L16 but with carry handles. We use an insulated 2
pole combiner block to run all the parallel conductors to the main 2/0
cable. No monitoring, but they do have an handy setup guide with
recommended settings, specific for each manufacturer (including Outback).
Note to all: Schneider XW can still not set its LVD above 48, which
basically makes it incompatible with most Li+ batteries. Their tech support
has been abysmal as well. We're looking forward to them as one of the
larger companies in the business, to put additional resources into their
engineering, and come out with at least a firmware update to correct this
problem.
Ray Walters
Remote Solar
303 505-8760
On 3/20/20 3:59 PM, David
Katz wrote: Hello Wrenches, I am working with some people that want to
use a 20 kw-hour to 30 kw-hour 48 volt lithium-ion battery with an Outback
Radian and Outback FM charge controllers. They are considering using
Discover, Blue-Ion, Battle Born or SimpliPhi batteries. Does any one have
any recommendations of which battery functions best with the Outback
system. Thanks, David Katz
_______________________________________________
List sponsored by Redwood
Alliance
List Address: RE-wrenches at lists.re-wrenches.org [3]
Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[4]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[5]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [6]
Check
out or update participant bios:
www.members.re-wrenches.org [7]
Links:
------
[1] http://members.sti.net/offgridsolar/
[2]
mailto:offgridsolar at sti.net
[3]
mailto:RE-wrenches at lists.re-wrenches.org
[4]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[5]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[6]
http://www.re-wrenches.org/etiquette.htm
[7]
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200321/7c76b5dd/attachment.htm>
More information about the RE-Wrenches
mailing list