[RE-wrenches] Ground mount fire code clarifications

Ray ray at solarray.com
Sat Mar 21 13:11:35 EDT 2020


I, second Jay's /no gravel/ sentiment.  I saw a huge 160 acre solar farm 
that they covered with hundreds of thousands of dollars of gravel.

Punch Line?  Only the weeds came back.  And only the nice 3 ft tall ones 
that some might call brush.....

Just use a weed eater or manually pull the taller stuff as needed a few 
times a year.  Smaller cordless weed eaters don't throw rocks as bad as 
the big motorized ones, and I would recommend clearing the rocks, not 
adding more.

Ray Walters
Remote Solar
303 505-8760

On 3/21/20 11:03 AM, Jay wrote:
> There is another aspect to the 10’ rule which is, its protection for 
> the array from wildfires. 10’ might not be enough for that though 
> depending on where you live.
>
> In regards to what’s being discussed, I have many ground mounts (not 
> talking pole mounts)out there, I try to have them as high off the 
> ground as practical, and to allow easy grass cutting. Yes brush would 
> have been removed before install.
> I don’t agree with bringing  gravel in, or any sort of barrier, we don 
> t need a sterile environment under the array.  And anyone who’s ever 
> seen such a weed cloth/gravel area will see it grass in over time, so 
> it really doesn’t work.
> Where I live, no fire danger in the winter after the rains, and during 
> the green grass of spring. Cut the grass as it drys, and as we get no 
> summer rain no more grass grows, until the following winter 
> rains,spring time.
>
> Many people live in green all year areas, Hawaii for example, or what 
> about if you have enough water to keep it all green?
>
> In the end it’s the AHJ’s world
>
> Jay
>
> Peltz power.
>
>
>
>
>
>
>
>
>
>> On Mar 20, 2020, at 7:28 PM, Martin Herzfeld <findsolar at herzfeld.org> 
>> wrote:
>>
>> 
>> Dan,
>>
>> I think there should more discussions on ground-mounted arrays as an 
>> option in addition to rooftop systems - to get out ahead of any 
>> issues.  In addition, any renderings for ground-mounted arrays and 
>> ground-mounted stuff as ESSs.
>>
>> 1.  By definition, a brush could mean a "slight and fleeting touch" - 
>> which we do not want to do at these times :) or "undergrowth, small 
>> trees and shrubs."
>>
>> 2.  The challenge also in one and and two family dwellings when there 
>> is a setback of only (3) three feet as an accessory structure and the 
>> (10) foot rule.
>>
>> 3.  I think mounts can be categorized in general as SPMs (Side of 
>> Pole Mounts), TPMs (Top of Pole Mounts), MPM's (Multiple Pole Mounts) 
>> or an Open Structure with the ability to walk underneath or a Closed 
>> structure where you can not walk underneath.
>>
>> 4. BTW, you may wish to look at versions of ISEP and the IRC too?
>>
>> "A.   RS402.4 (R324.6) Ground-mounted photovoltaic systems.
>>
>> Ground-mounted photovoltaic systems shall be designed and installed 
>> in accordance with Section (R301).
>>
>> B.  RS402.4.1 (R324.6.1) Fire separation distances.
>>
>> Ground-mounted photovoltaic systems shall be subject to the fire 
>> separation distance requirements determined by the local jurisdiction."
>>
>>
>> 5.  Gravel and the various types is also my goto soil amendment. In 
>> California, I'd also suggest working with a C27 Landscaping 
>> Contractor on what type of blue flowers would be okay.
>>
>>
>> What do you think?
>>
>>
>> All the best,
>>
>> Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified 
>> Master Trainer ™ for Photovoltaics (PV) Installation Professional 
>> #IREC 10037
>> Contract Training Provider (CTP)
>> Adjunct Professor, Energy
>>
>> California Solar & Electrical Contractor License #00833782  C46, C10, 
>> D56, D31, C-7
>> Solar, Electrical, Trenching, Pole Installation & Maintenance, 
>> Instrumentation
>>
>> Contract Solar (PV) Technical Inspector - 3rd Party Inspections
>> Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
>> OSHA-Authorized Construction Trainer #32-0105338
>> CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG
>>
>> * Professional Member, International Association of Electrical 
>> Inspectors  #7035507
>> * Accredited and Registered North American Board of Certified Energy 
>> Practitioners (NABCEP) Continuing Education (CE) Provider
>>
>> Telephone & Text: 510.243.0190
>>
>> On Fri, Mar 20, 2020, 4:06 PM Dan Fink <danbob88 at gmail.com 
>> <mailto:danbob88 at gmail.com>> wrote:
>>
>>     Hello esteemed Wrenches; I am trying to clear this up for a
>>     client and his AHJ, which is also puzzled at how to interpret IFC
>>     2018, Section 1204.4, which states:
>>
>>         Setback requirements shall not apply to ground-mounted,
>>         free-standing photovoltaic arrays. A clear, brush-free area
>>         of 10 feet (3048 mm) shall be required for ground-mounted
>>         photovoltaic arrays.
>>
>>     I found one lone informational note in a white paper stating this
>>     was to prevent a burning PV array from igniting surrounding
>>     vegetation and the fire spreading.
>>
>>     So, has anyone dealt with an AHJ on this before? Our questions are:
>>
>>       * What exactly is a "free-standing photovoltaic array" that is
>>         exempt? A pole mount? Couldn't burning debris from that
>>         ignite vegetation underneath?
>>       * What exactly does "A clear, brush-free area of 10 feet (3048
>>         mm)" mean? "10 feet" is a linear measurement, not an area,
>>         that would be in square feet.
>>       * What is "brush"? Does grass count as brush?
>>
>>     I would interpret this on the safe side as meaning that all
>>     vegetation under the PV array and out to a 10 foot perimeter
>>     should be cleared, except for pole-mount arrays (that exception
>>     makes no sense to me).
>>
>>     I always recommend to clients that the area /under/ the ground
>>     mount array should be pea gravel bordered by railroad ties, but
>>     out to 10 feet from the array edge seems excessive.
>>
>>     Any input greatly appreciated!
>>
>>     Dan Fink
>>     Executive Director, Buckville Energy Consulting
>>     NABCEP PV Associate
>>     NABCEP Certified PV System Inspector
>>     IREC Certified Instructor™ for:
>>     ~ PV Installation Professional
>>     ~ Small Wind Installer
>>     NABCEP Registered Continuing Education Providers
>>     d <mailto:dan.fink at greendustrialtraining.com>anbob88 at gmail.com
>>     <mailto:anbob88 at gmail.com>
>>     970-672-4342
>>
>>     _______________________________________________
>>     List sponsored by Redwood Alliance
>>
>>     List Address: RE-wrenches at lists.re-wrenches.org
>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>>     Change listserver email address & settings:
>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>     List-Archive:
>>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>     List rules & etiquette:
>>     www.re-wrenches.org/etiquette.htm
>>     <http://www.re-wrenches.org/etiquette.htm>
>>
>>     Check out or update participant bios:
>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200321/2347966d/attachment.htm>


More information about the RE-Wrenches mailing list