[RE-wrenches] Generator surging
Mac Lewis
maclewis1 at gmail.com
Thu Mar 19 10:01:00 EDT 2020
Do you hear audible changes in generator rpm?
I believe that generator has the RDC2 controller that you can log into with
Sitetech. There is a parameter that adjusts the sensitivity of the governor
(I can dig up the exact parameter later). A Kohler tech can adjust this and
I'm betting it will help, or at least rule out the generator control loop.
What's your altitude?
On Thu, Mar 19, 2020, 1:20 AM William Miller <william at millersolar.com>
wrote:
> Mac:
>
>
>
> I know well what the AC input mode is. This is the project that had the
> excessive THD on the voltage waveform (>26%f). Here is a link
> <https://millersolar.com/MillerSolar/case_studies/25_GFI%20Tripping/GFI_Tripping.html>
> to the case study.
>
>
>
> As you can see, we resolved the problem by changing the AC input mode to
> Backup. After recent rains started and generator run became necessary, the
> client started noticing flickering of lights and refrigerator operation was
> unreliable. We examined the E-Gauge data and could see rapid fluctuations
> in the generator output. At one point we saw generator power range from
> 19kW to 12Kw and back in about 2 seconds.
>
>
>
> We isolated the generator into a load bank and it was rock solid. We
> tried lots of things but when we reconnected the generator to the Radians
> and switched to the Radians to Generator input mode the surging stopped.
> Unfortunately, the Generator mode causes tons of THD, as noted in the case
> study.
>
>
>
> So we can’t use Generator because of THD, and we can’t use Backup (or
> Support or UPS) because in all these modes the generator surges.
>
>
>
> By the way, this is a newish Kohler 30RCL. This should be a rock-solid
> match to a 24 kW Radian system.
>
>
>
> Like I said, we tried lots of things. What stopped the surging was to
> open the AC input breaker to Inverter 1. It did not help to open the input
> to Inverters 2 or 3. I don’t have a clue as to why this is so…
>
>
>
> We tried taking Inverter 1 out of the system--moving inverter 2 up to
> Master and Inverter 3 to Slave 1. The generator still surged. So if anyone
> started to think Inverter 1 was the problem, this was not confirmed.
>
>
>
> We are certain the neutral bonding is exactly as it should be. We tripled
> checked this when chasing the THD problems. We also adjusted input AC from
> 30 to 50 (per port), no improvement.
>
>
>
> I must say Outback has been very available to us as we try to figure these
> problems out. I am fortunate that I am working with a senior engineer. We
> are both currently stumped, but we are going to consult again tomorrow and
> see if any other ideas come to us.
>
>
>
> Thanks everyone for the input. More soon.
>
>
>
> William Miller
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Mac Lewis
> *Sent:* Wednesday, March 18, 2020 6:35 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Generator surging
>
>
>
> Hi William,
>
>
>
> Do you know what your AC input mode is?
>
> I'd try playing with this mode.
>
> If you have a generator, I'd try switching between "generator",
> "support". You may quickly see a difference. There is a small diode
> symbol that shows up on the Mate3s screen during generator charging. I
> don't fully understand what that means but I know that it can affect how a
> generator works with the Radian.
>
>
>
> Also, you may try lowering the charging current and see how the generator
> responds.
>
>
>
> What type of generator? Whats your AC input limits?
>
>
>
> On Wed, Mar 18, 2020 at 6:56 PM Jerry Shafer <jerrysgarage01 at gmail.com>
> wrote:
>
> Adjust the generator max output in the outback down and see what happens
>
> Jerry
>
>
>
> On Wed, Mar 18, 2020, 4:04 PM William Miller <william at millersolar.com>
> wrote:
>
> Friends:
>
>
>
> I have a 24kW Radian system that is acting up. The problem is when the
> generator is running, it surges. Voltage and power go up and down. We
> connected the generator to a load bank and there was no surging. This
> makes me think the problem is in the Radian system.
>
>
>
> Has anyone else experienced this?
>
>
>
> Thanks in advance for any input.
>
>
>
> William Miller
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
>
> --
>
>
>
>
>
>
>
> Mac Lewis
>
> "Yo solo sé que no sé nada." *-Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200319/2a5655ad/attachment.htm>
More information about the RE-Wrenches
mailing list