Hugh....Typically the temp Sense warning is not related to an external temp
sensor, rather an internal temperature sensor. The Outback inverters
typically will run normally even with this temp sensor not working. I
believe it is related to temperature of one of the boards and relates to
turning the cooling fan on if present - normally it is not related to a
battery temp sensor which is what I got the impression you understood it to
be. However, typically this will show up as a red blinking error light
which signifies a warning instead of a solid red error light during which
the inverter may stop working.
Sunny Regards,
Kirpal Khalsa
Oregon LRT#25
NABCEP Certified PV Installation Professional
Oregon Solarworks LLC
www.oregonsolarworks.com
541-299-0402
On Mon, Mar 9, 2020 at 10:00 AM Kent Osterberg <kent at coveoregon.com> wrote:
> Hugh,
>
> I've seen these symptoms before. The problem was a failed output relay on
> the ac board.
>
> Kent Osterberg
> Blue Mountain Solar
>
>
> On 3/9/2020 9:25 AM, Hugh Piggott wrote:
>
> Hi Wrenches,
>
> I wonder if anyone can tell me what is happening here?
>
> I have an Outback VFX that I used for my own home from 2006-2018. It’s a
> 50Hz 240V unit, but similar otherwise to any other 48V VFX. It was working
> well when disconnected. I needed to replace the inverter system for other
> reasons.
>
> I installed this for a neighbour recently on his 48V system, and it
> apparently worked when I left the building.
>
> Now it’s not working. When “off” it shows a warning for temperatures
> sensor - fair enough I did not install one. Maybe when it gets connected
> to a generator it will be found a sensor. This is the only error or fault
> with a yes.
>
> When “on” it makes a reassuring buzz and both lights come up green and
> there is no error or warning in the Mate. Just one problem - no output.
>
> Another weird thing. I go to the status menu and check meters
> STATUS/FX/METER output voltage and it says “4V”. So it *knows* that it
> is not working but it appears to have no qualms or misgivings about this
> state of affairs. NO error, no warning, two green lights.
>
> I tried rebooting with the battery fuse. I tried resetting to factory
> defaults. No joy.
>
> I suppose I will take it to pieces and try to figure out a hardware
> failure but I wonder if anyone has seen this and can give me a clue?
>
> cheers
> Hugh
>
>
> Hugh Piggott
> Scoraig Wind Electric
> Dundonnell
> Ross shire
> IV23 2RE, UK
> +44 77 1315 7600
> hugh at scoraigwind.co.uk
> www.scoraigwind.co.uk
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200309/de688468/attachment.htm>
More information about the RE-Wrenches
mailing list