You should be able to go to 32kW with four Outback Radians. I agree, there
are not enough 32-100kW split phase inverter system options. With LiPO
batteries becoming popular, a high integrated charging capacity is
desirable in larger battery capacity scenarios, especially if trying to
maximize generator efficiency through reduced run time.
On Sun, Feb 23, 2020 at 12:03 PM Jeff Clearwater <
jeffc at villagepowerdesign.com> wrote:
> The Victron Quattro (120/240) is stackable to 6 units for 30 KW of split
> phase or 48 KW of 240V and 144KW of 3 phase if I’m reading the spec sheets
> correctly.
>
> Sent from my iPhone
>
> On Feb 23, 2020, at 6:42 AM, Jay <jay.peltz at gmail.com> wrote:
>
> People might also look at Victron inverters.
>
> Jay
> Peltz Power.
>
> On Feb 23, 2020, at 3:23 AM, Jeff Clearwater <jeffc at villagepowerdesign.com>
> wrote:
>
> The Sol-Ark manual indicates 240 Volt stacking to 8 units (9 units for
> 208V). They list the "12KW" off-grid output as 8 KWs each. So 64 KWs.
>
> anybody stacked a signficant number of them yet?
>
> Looking forward to hearing feedback from experienced installers.
>
> Best,
>
> Jeff
>
>
> Allan Sindelar wrote on 2/22/20 6:56 PM:
>
>
> Jeff, according to Midnite’s website, their B-17 inverter can be up to 40
> kW in 2 kW increments.
> Allan
>
> On Feb 22, 2020, at 8:05 PM, Jeff Clearwater
> <jeffc at villagepowerdesign.com> <jeffc at villagepowerdesign.com> wrote:
>
> Ahh you're right all our 120/240 volt systems are less than 24 KW. I
> was thinking of 230 V 50hz systems with multi-cluster boxes.
>
> How large can the Sol-Ark be stacked to? Anyone with large Sol-Ark system
> experience?
>
> I hear Mornignstar and MidNite are working on surge capable off-grid
> inverters. Anyone have a insight as to their KW goals?
>
> Best,
>
> Jeff
>
> wes kennedy wrote on 2/21/20 1:37 PM:
>
> Hi Jeff,
>
> I think the biggest split phase sunny island system is 4 units, so that's
> 24KW.
>
> What do you do for larger systems? Segment the loads? Not always very
> practical.
>
> This latest opportunity is for an agricultural building that peaks at
> 75KW.
>
>
>
> -Wes Kennedy 303-653-3073
>
>
> On Friday, February 21, 2020, 12:47:39 PM MST, Jeff Clearwater
> <jeffc at villagepowerdesign.com> <jeffc at villagepowerdesign.com> wrote:
>
>
> All of my SMA Sunny Island Sunny Boy AC coupled systems greater than 12 KW
> have worked flawlessly and delivered reliable power and good monitoring for
> years. Less excited about my Schneider and Outback systems due to
> callbacks and hassles. a bit more expensive but worth it IMHO.
>
> Hope that helps!
>
> Jeff
>
> wes kennedy wrote on 2/21/20 9:41 AM:
> Hi friends,
>
> I keep running across opportunities with 50KW-300KW peak load
> requirements, on split phase services. Big homes, agriculture etc.
>
> Outback, Schneider, SMA can all gang/stack into the 30-50KW range, but
> north of there, I am not finding many (any?) options?
>
> Just found Aims Power 50 KW split phase unit with claims of higher power
> offerings by special order. Even the 50KW unit is $20K, so quite spendy.
> Any experience with these guys?
> 50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc TO
> 220/230/240 Vac
> <https://mailtrack.io/trace/link/4f7d32cc7dfc2842fab2bf9bea74770d093aa180?url=https%3A%2F%2Fwww.aimscorp.net%2F50kw-50-000-watt-dc-to-ac-pure-sine-power-inverter-charger-384-vdc.html&userId=1613865&signature=4c8e36397e811f06>
>
>
>
>
> 50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc TO ...
>
> 50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc Split
> Phase 220/230/240
>
> <https://mailtrack.io/trace/link/216c9b2fbb26a7942bdc584da32840a0a0ef7fd7?url=https%3A%2F%2Fwww.aimscorp.net%2F50kw-50-000-watt-dc-to-ac-pure-sine-power-inverter-charger-384-vdc.html&userId=1613865&signature=946f0bcf0459019e>
>
>
> Thanks for any input!
>
> -Wes Kennedy 303-653-3073
> on this list since the 90's
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <https://mailtrack.io/trace/link/d63d3e3a978e8a87add1f7501d59ee5f5fb38a4f?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4973675a4c4ab420>
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <https://mailtrack.io/trace/link/7a023e95bffe7d2040feac93f95e0a0f11fa6987?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=46b10739ff5fd8bf>
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm <https://mailtrack.io/trace/link/331c727f2364456812baea8d1c52d3f40beb8a90?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=e719e1d05b5cf87c>
>
> Check out or update participant bios:www.members.re-wrenches.org <https://mailtrack.io/trace/link/5bb69b1b7b0444267f727e13eb46e364a9678425?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=957b8e96e1dc8c0b>
>
>
> --
> ~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> linkedin
> <https://mailtrack.io/trace/link/bd394429f8487d697d00a1e7111da004066652d3?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Fjeff-clearwater-0622a312%2F&userId=1613865&signature=36a1593bd28b8ccd>
> www.villagepowerdesign.com
> <https://mailtrack.io/trace/link/cecd4177686007dbcca9514d9fe8dace135819a2?url=http%3A%2F%2Fwww.villagepowerdesign.com&userId=1613865&signature=1d41a5257aa87e38>
> cell - 413-559-9763
> ~~~~~~~~~~~~~~~~~~~~~~~
>
>
>
> --
> ~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> linkedin
> <https://mailtrack.io/trace/link/c380a264fce7d248a05288cd74b288d2284afd86?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Fjeff-clearwater-0622a312%2F&userId=1613865&signature=0979b1caceaf1f78>
> www.villagepowerdesign.com
> <https://mailtrack.io/trace/link/3404019e669b4ea32e8ec188a6f79c661abb162a?url=http%3A%2F%2Fwww.villagepowerdesign.com&userId=1613865&signature=4df2961ce5ac7182>
> cell - 413-559-9763
> ~~~~~~~~~~~~~~~~~~~~~~~
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/885b9b3aa7dcee55c3030e4c1ac895732d0f9476?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=8f65292e04db6d22>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://mailtrack.io/trace/link/22484a017da9b2eebda0840b01f4505fd97cb56a?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=a94f136f8720e27b>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/0dffba0ee72532b58372452ce5beb1bae3ba7e59?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=ff4d9ed34e66d68e>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/d4456b7a80863a1217d1086fe7653505897d9538?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=8f0b6b1530f7ed66>
>
>
>
> --
> ~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> linkedin
> <https://mailtrack.io/trace/link/5e21bee273ab6ea4ea7bb66af2f6a77bba39d0e4?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Fjeff-clearwater-0622a312%2F&userId=1613865&signature=67970ca7721852f4>
> www.villagepowerdesign.com
> <https://mailtrack.io/trace/link/25079fe30279c8e43717988138da7a1d6a849278?url=http%3A%2F%2Fwww.villagepowerdesign.com&userId=1613865&signature=f94c7714ce45bcb0>
> cell - 413-559-9763
> ~~~~~~~~~~~~~~~~~~~~~~~
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/7faad24744f7836e52eb63cdd3a76a23937d9e54?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=21af3aeef94a045b>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://mailtrack.io/trace/link/f41cc1c5b8afe2e101843a6b8ec945448ece91a5?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=45e6f26912d973bb>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/b7f9144a00a6cf0b4d6f2bd681111b53a6595f2e?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=088a691258bf6bd1>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/2d2f5cd7b9bb563906971321e447e25526729513?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=160320716001b611>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/ebd1d876c5b86898cb21857244c50fc53146cb96?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=57c4997a6aa1dbab>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://mailtrack.io/trace/link/6fda109b28cb801bcbaed4a78cee18a7e17ee42f?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=d1de0d71cffe8980>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/ce5dcc918dfb2fa6cfd75d08dde8184ca14e53a8?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=35554bed0717d9b9>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/703ff1acec2d0f28815a2ab2d7b103da71aa4216?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=e961529dbea97b88>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200223/a6ce8a3a/attachment.htm>
More information about the RE-Wrenches
mailing list