Hi August,
Ganging multiple units gets pretty unworkable at a certain point. I actually have a friend here in Colorado who had Tesla engineered in on a 9 power wall system. They backed out and said they wouldn't support it, due to potential instability. 
(Also, I'm working primarily with Blue Planet Energy these days, so really looking for the missing inverter piece).
Thanks! 
-Wes Kennedy 303-653-3073 

    On Friday, February 21, 2020, 02:52:49 PM MST, August Goers <august at luminalt.com> wrote:  
 
 The Tesla Powerwall system has worked well for us, and be configured up in the 50 kW + range. We've installed several 4-Powerwall systems totalling 20 kW / 54 kWh. In order to get to 50 kW battery inverter capacity, you'd need 10 Powerwalls. Now you can do multiple Gateways on site, so could conceivably do 20 + Powerwalls on a single site.
AugustLuminalt
On Fri, Feb 21, 2020 at 11:47 AM Jeff Clearwater <jeffc at villagepowerdesign.com> wrote:

All of my SMA Sunny Island Sunny Boy AC coupled systems greater than 12 KW have worked flawlessly and delivered reliable power and good monitoring for years.  Less excited about my Schneider and Outback systems due to callbacks and hassles.  a bit more expensive but worth it IMHO.

Hope that helps!

Jeff

wes kennedy wrote on 2/21/20 9:41 AM:

 Hi friends,
I keep running across opportunities with 50KW-300KW peak load requirements, on split phase services. Big homes, agriculture etc. 
Outback, Schneider, SMA can all gang/stack into the 30-50KW range, but north of there, I am not finding many (any?) options? 
Just found Aims Power 50 KW split phase unit with claims of higher power offerings by special order. Even the 50KW unit is $20K, so quite spendy. Any experience with these guys? 50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc TO 220/230/240 Vac

| 
| 
| 
| 
 | 
 |

 |

 |
| 
| 
 | 
50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc TO ...

50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc Split Phase 220/230/240
 |

 |

 |



Thanks for any input! 
-Wes Kennedy 303-653-3073on this list since the 90's 
  
 _______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



-- 
~~~~~~~~~~~
 Jeff Clearwater
 Village Power Design
 linkedin 
 www.villagepowerdesign.com
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


  
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200221/07762d20/attachment.htm>


More information about the RE-Wrenches mailing list