Need to edit this post: The micro inverters are UL listed for grid 
connected operation.

What I've noticed is that most of the AIMS inverters are not UL, ETL, or 
otherwise third-party tested. And none seam to be designed for utility 
interactive operation.

Kent Osterberg
Blue Mountain Solar


On 2/21/2020 1:37 PM, wes kennedy wrote:
> Hi Jeff,
>
> I think the biggest split phase sunny island system is 4 units, so 
> that's 24KW.
>
> What do you do for larger systems? Segment the loads? Not always very 
> practical.
>
> This latest opportunity is for an agricultural building that peaks at 
> 75KW.
>
>
>
> -Wes Kennedy 303-653-3073
>
>
> On Friday, February 21, 2020, 12:47:39 PM MST, Jeff Clearwater 
> <jeffc at villagepowerdesign.com> wrote:
>
>
> All of my SMA Sunny Island Sunny Boy AC coupled systems greater than 
> 12 KW have worked flawlessly and delivered reliable power and good 
> monitoring for years. Less excited about my Schneider and Outback 
> systems due to callbacks and hassles.  a bit more expensive but worth 
> it IMHO.
>
> Hope that helps!
>
> Jeff
>
> wes kennedy wrote on 2/21/20 9:41 AM:
> Hi friends,
>
> I keep running across opportunities with 50KW-300KW peak load 
> requirements, on split phase services. Big homes, agriculture etc.
>
> Outback, Schneider, SMA can all gang/stack into the 30-50KW range, but 
> north of there, I am not finding many (any?) options?
>
> Just found Aims Power 50 KW split phase unit with claims of higher 
> power offerings by special order. Even the 50KW unit is $20K, so quite 
> spendy. Any experience with these guys?
> 50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc 
> TO 220/230/240 Vac 
> <https://www.aimscorp.net/50kw-50-000-watt-dc-to-ac-pure-sine-power-inverter-charger-384-vdc.html> 
>
>
>
> 	
>
>
> 	
>
>
>     50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384
>     Vdc TO ...
>
> 50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc 
> Split Phase 220/230/240
>
> <https://www.aimscorp.net/50kw-50-000-watt-dc-to-ac-pure-sine-power-inverter-charger-384-vdc.html>
>
>
> Thanks for any input!
>
> -Wes Kennedy 303-653-3073
> on this list since the 90's
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address:RE-wrenches at lists.re-wrenches.org  <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org  <http://www.members.re-wrenches.org>
>
>
> -- 
> ~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
> www.villagepowerdesign.com <http://www.villagepowerdesign.com>
> cell - 413-559-9763
> ~~~~~~~~~~~~~~~~~~~~~~~
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200221/bc994c1a/attachment.htm>


More information about the RE-Wrenches mailing list