Hi Jon, my take is the absorb is way too short, the array is way too small,
The solar period is over before the batteries are charged.  I would set
absorb at 28.8 Volts,  6 hrs, because the winter days are short.  I do not
know how to set charge max amps with paralleled controllers.  Then set back
to normal for after equinox.

On Tue, Feb 18, 2020 at 10:37 PM Jon Siegenthaler <
jon.siegenthaler at gmail.com> wrote:

> Hey Wrenches,
>
> I just did a site visit for a client who's had a few iterations of PV
> installed. The main reason for the call was that the battery bank would
> never charge to 100%SOC but rather appear to charge to 100%SOC and actually
> hover around 70%SOC. At  the end of the day the client would top it off
> with the generator for 30-60min. This has been happening since October, I
> just got the call the other day.
>
> The site is less than code compliant to say the least and the programming
> of the 3 charge controllers were not equal.
>
> Array 1 South Facing 4-Canadian 250w (one string)
> Flexmax 80
> Absorb 29.3V 6hrs
> Float 27.3
> End Amps 10A
> Rebulk 25V
>
> Array 2 South Facing 6-205w 2-195w (one string)
> Flexmax 60
> Absorb 29.3V 6hrs
> Float 27.3
> End Amps 10A
> Rebulk 25.6V
>
> Array 3 North Facing 8-295w Renosola (4 strings)
> Flexmax 80
> Absorb 29.4 1hr
> Float 27.3
> End Amps 0
> Rebulk 24
>
> 20-Trojan Reliant L16 12V (5 parallel to a bus) purchased the end of 2017
>
> Apart from the not so great design to say it lightly, the bank is
> consistently showing a stepping voltage of about 70%SOC up to 100%SOC from
> negative to positive. I changed the charge controllers to an equal
> absorption voltage and time (28.8V and 4hrs) to try and slowly bring up the
> lagging side of the bank. I was cautious not to raise them all to 29.4 at
> 4+hrs because I don't know their history and didn't want to cook them
> further if they are indeed headed that way. At the time of inspection the
> batteries were about 84F and the thermal camera showed no variations or hot
> spots.
>
> I asked the owner to report back if it gets better, worse, or the same. He
> reported back and said that the total kWh production daily is gradually
> going down over these past few days. Any suggestions on how to bring this
> bank back to 100%SOC would be appreciated.
>
> Jon Siegenthaler
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200219/cb42033c/attachment.htm>


More information about the RE-Wrenches mailing list