[RE-wrenches] largest 240v GT inverter
Jeff Clearwater
jeffc at villagepowerdesign.com
Mon Feb 10 02:22:09 EST 2020
Hey Jay,
Why not just use 8 SMA SB 7.7's = 61.6 KW rated, 32 Amps 240 each.
Then use a dedicated 320 Amp Rated (Typical nominal bus of a 400 A
panel) Supply Side fed Breaker panel as you'll have 256 x 1.25 Amps of
Solar bus = 320 - right at the limit but you are good to go!
Jeff
Chris Sparadeo wrote on 2/8/20 7:42 PM:
> Jay,
>
> Sorry, I missed the 120/240v part. That CPS product is 3 phase.
> Fronius has the Primo 15kW in split phase. Have had good luck with them.
>
> On Sat, Feb 8, 2020 at 10:30 PM Chris Sparadeo
> <sparadeo.chris at gmail.com <mailto:sparadeo.chris at gmail.com>> wrote:
>
> Hi Jay,
>
> CPS has a 60 kW -1000v string inverter that might be a good fit
> for your project.
>
> https://www.chintpowersystems.com/commercial-60kw.shtml
>
>
> Best,
>
> Chris
>
> On Sat, Feb 8, 2020 at 8:54 PM jay <jay.peltz at gmail.com
> <mailto:jay.peltz at gmail.com>> wrote:
>
> HI All,
>
> I’m wondering what the largest GT battery less inverter (and
> what people recommend) for 240v 60hz is out there.
>
> I don’t need MLPE, as project would be ground mount, its large
> residential, potentially 60KW.
>
> SE has their 11.4KW, but I’ve heard lots of bad things about
> them recently.
> Fronius has a 10KW?
>
> Thanks in advance
>
>
> jay
>
> Peltz power
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
>
> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
--
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200209/de800b7b/attachment.htm>
More information about the RE-Wrenches