[RE-wrenches] Problems with Conext SW inverter
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Tue Feb 4 17:33:09 EST 2020
No problems that I know of and about 15 that work fine. I only use the
XW for my clients but many out there.
You said the voltage decreased
below absorb when you tried, EQ will not start unless it has gone thru
absorb to float.
The work around to start EQ without going thru the cycle
is to program a bulk, absorb, and float for the EQ voltage.
Other ways
also like shortening absorb time to one minute.
You also know that you
should never EQ a battery that is not charged without monitoring bat temp
and being on site.
EQ does have to be enabled in set-up BTW. It is not
the firmware either unless it was a botched update.
Do not forget to
reprogram any changes you make! Good Luck!
DAVE ANGELINI OFFGRID
SOLAR
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
[1]
e-mail offgridsolar at sti.net [2]
text 209 813 0060
On Tue, 4 Feb 2020
13:52:40 -0800, Eric Smiley wrote: It is of grid and, yes, the generator
was running when I attempted to equalize.
Schneider has no solution and it
is just outside the 2 year warranty. I am going to try a couple of things
when I go back:
* setting the battery type to the default for FLA
battery - it is set to Custom battery right now;
* installing an older
firmware version, to see if it is just a bug in the last update.
However, based on the condition of the battery, I suspect the client has
never been able to properly equalize; despite thinking they were doing
everything properly. A real shame they even released this inverter to the
market. This will likely be the third and last CSW that we end up replacing
with a Magnum. If anyone else has had issues with the CSW, I'd like to
know. We know other installers that believe this was a defective product
from the beginning and would like to press Schneider to compensate clients
and installers who have wasted far too much time and money trying to make
it work as promised.
Eric Smiley, P.Eng.
Project Manager,
North Island
E: eric at vecoop.ca [3]
T: 1-888-386-0116 ext 702 (toll
free)
C: 250-703-6004
W: viridianenergy.ca [4]
RENEWABLE POWER NOW
On Fri, 31 Jan 2020 at 11:56, Maverick Brown wrote: Is this
an off grid system? If so, the generator needs to be running to execute EQ
on the inverter.
Thank you, Maverick
On Jan 31, 2020, at 1:50 PM,
Eric Smiley wrote:
I recently discovered a critical problem with a
client's SW inverter and I want to know if others have encountered this.
It's an SW4024 with Flooded Lead Acid batteries. The system is configured
using the Custom Battery setting: Bulk and Absorption are set to 29.2 V.
Equalize is set to 32 V. The problem is when Equalize is enabled, the
system goes through Bulk and Absorption just fine. However, when it
switches to Equalize it doesn't actually equalize. What I observed was the
voltage actually decreased to 0.5 V below the Absorption Voltage setting.
Eric Smiley, P.Eng.
Project Manager, North Island
E: eric at vecoop.ca
[8]
T: 1-888-386-0116 ext 702 (toll free)
C: 250-703-6004
W:
viridianenergy.ca [9]
RENEWABLE POWER NOW
_______________________________________________
List sponsored by Redwood
Alliance
List Address: RE-wrenches at lists.re-wrenches.org [11]
Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[12]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[13]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [14]
Check
out or update participant bios:
www.members.re-wrenches.org [15]
_______________________________________________
List sponsored by Redwood
Alliance
List Address: RE-wrenches at lists.re-wrenches.org [16]
Change
listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [17]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[18]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [19]
Check out or update participant bios:
www.members.re-wrenches.org [20]
Links:
------
[1] http://members.sti.net/offgridsolar/
[2]
mailto:offgridsolar at sti.net
[3] mailto:eric at vecoop.ca
[4]
http://www.viridianenergy.ca
[5] http://www.viridianenergy.ca/
[6]
mailto:maverick at mavericksolar.com
[7] mailto:eric at vecoop.ca
[8]
mailto:eric at vecoop.ca
[9] http://www.viridianenergy.ca
[10]
http://www.viridianenergy.ca/
[11]
mailto:RE-wrenches at lists.re-wrenches.org
[12]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[13]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[14]
http://www.re-wrenches.org/etiquette.htm
[15]
http://www.members.re-wrenches.org
[16]
mailto:RE-wrenches at lists.re-wrenches.org
[17]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[18]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[19]
http://www.re-wrenches.org/etiquette.htm
[20]
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200204/19e45cd3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: blocked.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200204/19e45cd3/attachment.gif>
More information about the RE-Wrenches
mailing list