[RE-wrenches] Inverter Output Circuit OCPD Meltdown
Blake Gleason
blake at sunlightandpower.com
Wed Jan 22 18:15:04 EST 2020
Thanks for sharing, Jason. That's an excellent cautionary tale...
On Wed, Jan 22, 2020 at 2:58 PM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:
> I discovered the issue I believe, so I thought I'd update all of you who
> gave me ideas on what to look for (thank you).
>
> And this is something that I stress the importance of all the time...
>
> The branch circuit pairs were not properly paired up! All of the L1
> conductors went to L1 on the bus and all of the L2 to L2. However, for
> example, circuit 1 L1 and circuit 2 L2 were on a single 2-pole breaker. And
> circuit 2 L1 and circuit 1 L2 were on another breaker. Everything worked
> because it was electrically connected to the right bus bar. However, when
> there was a previous fault one of the breakers probably didn't trip when it
> should have as a result of the improper pairings. It was reset a few times
> and just kept heating up and heating up.
>
> This isn't conclusive, but it sure makes sense. It wasn't fun tracking
> this down with 5 strings and 5 junction boxes on the roof, but once we
> started continuity testing and finding strange results, it became clear.
>
> Jason Szumlanski
>
>
>
> On Tue, Jan 21, 2020 at 12:10 PM Jason Szumlanski <
> jason at floridasolardesigngroup.com> wrote:
>
>> (System installed by another contractor...)
>>
>> I have been tasked with assisting in the investigation of damage in a
>> subpanel used to combine inverter output circuits (5 strings of
>> microinverters). There appears to be no damage to conductors or other
>> system components. It looks like the damage started at the stabs of the bus
>> bar where the breakers connect. Picture attached. Here are a few clues:
>>
>> - Monitoring indicates that damage occurred overnight a few weeks
>> ago. That night we had rain as a winter front came through Florida,
>> possibly lightning. The prior day everything was fine.
>> - The next morning, only 2 of 5 strings started producing power, but
>> 4 of 5 strings were reporting data to the Envoy. The two strings that were
>> reporting but not producing power reported 0Vac and Voc on the DC side of
>> the microinverters.
>> - A couple of weeks later, 1 of the 2 strings that was producing
>> power quit doing so, but continued reporting data.
>> - Customer discovered damage yesterday.
>> - About a week before the initial damage apparently manifested
>> itself, another contractor installed a whole house generator transfer
>> switch on the line side of the PV interconnection. The generator has never
>> been run (there is not even a LP fuel source on site yet). I pointed out
>> that the solar interconnection, which was previously on the supply side,
>> would need to be moved to the supply side of the generator transfer
>> switch's main breaker before operation. During the transfer switch
>> installation, the contractor also switched line 1 and line 2, but that
>> shouldn't really matter, except for Enphase consumption monitoring, which
>> was messed up by the swapping of the lines.
>>
>> So I'm looking for ideas. I'm wondering if the OCPD would be a likely
>> place for lightning damage to manifest itself. I can't visually detect any
>> other damage anywhere else. I can't imagine that the transfer switch
>> installation would have anything to do with it, but the timing is
>> interesting. Other than replacing the subpanel and OCPD and firing it back
>> up (no pun intended), I'm not sure how to approach further investigation.
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
--
Blake Gleason, PE | Employee Owner
Director of Innovation and Technical Excellence
O: 510-845-2997 x128
C: 510-867-5878
1035 Folger Ave.
Berkeley, CA 94710
www.sunlightandpower.com
License #326203
<https://bcorporation.net/> <https://www.amicussolar.com/>
<https://calssa.org/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200122/08b8d8bb/attachment.htm>
More information about the RE-Wrenches