[RE-wrenches] Inverter Output Circuit OCPD Meltdown
Jerry Shafer
jerrysgarage01 at gmail.com
Tue Jan 21 14:51:57 EST 2020
Wrenches
Cant tell anymore but l had a buss failure due to water getting on buss and
pealing the tin off the buss and the aluminum base will light up real quick.
Jerry
On Tue, Jan 21, 2020, 9:10 AM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:
> (System installed by another contractor...)
>
> I have been tasked with assisting in the investigation of damage in a
> subpanel used to combine inverter output circuits (5 strings of
> microinverters). There appears to be no damage to conductors or other
> system components. It looks like the damage started at the stabs of the bus
> bar where the breakers connect. Picture attached. Here are a few clues:
>
> - Monitoring indicates that damage occurred overnight a few weeks ago.
> That night we had rain as a winter front came through Florida, possibly
> lightning. The prior day everything was fine.
> - The next morning, only 2 of 5 strings started producing power, but 4
> of 5 strings were reporting data to the Envoy. The two strings that were
> reporting but not producing power reported 0Vac and Voc on the DC side of
> the microinverters.
> - A couple of weeks later, 1 of the 2 strings that was producing power
> quit doing so, but continued reporting data.
> - Customer discovered damage yesterday.
> - About a week before the initial damage apparently manifested itself,
> another contractor installed a whole house generator transfer switch on the
> line side of the PV interconnection. The generator has never been run
> (there is not even a LP fuel source on site yet). I pointed out that the
> solar interconnection, which was previously on the supply side, would need
> to be moved to the supply side of the generator transfer switch's main
> breaker before operation. During the transfer switch installation, the
> contractor also switched line 1 and line 2, but that shouldn't
> really matter, except for Enphase consumption monitoring, which was messed
> up by the swapping of the lines.
>
> So I'm looking for ideas. I'm wondering if the OCPD would be a likely
> place for lightning damage to manifest itself. I can't visually detect any
> other damage anywhere else. I can't imagine that the transfer switch
> installation would have anything to do with it, but the timing is
> interesting. Other than replacing the subpanel and OCPD and firing it back
> up (no pun intended), I'm not sure how to approach further investigation.
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200121/e806a1ae/attachment.htm>
More information about the RE-Wrenches
mailing list