[RE-wrenches] Inverter Output Circuit OCPD Meltdown
Jason Szumlanski
jason at floridasolardesigngroup.com
Tue Jan 21 13:16:07 EST 2020
Yes - It's only 56A total inverter output rating on a 125A bus. Max string
is 13A inverter output rating on 20A OCPD.
On Tue, Jan 21, 2020 at 12:58 PM Chris Sparadeo <sparadeo.chris at gmail.com>
wrote:
> Jason,
>
> Have you calculated your back-fed amapacity allowance to confirm it
> complies with the 120% busbar rule as per 705.12?
>
> Best,
> Chris
>
> On Tue, Jan 21, 2020 at 12:40 PM August Goers <august at luminalt.com> wrote:
>
>> Hi Jason -
>>
>> It certainly appears that there was some sort of surge or short. We've
>> had a few cases where microinverter branch circuit end termination caps
>> were left off or fell off and shorted out during rain storms. You might
>> want to double check that those are all in place. We've also had cases were
>> microinvers themselves developed internal shorts. This third comment is
>> only anecdotal - I've been in touch with a couple of other installers that
>> have had back-fed breaker issues specifically with Eaton brand breakers
>> burning up the bus stabs. Our company has had one unexplained issue where
>> the inverter output breaker bus stabs were burned up with Eaton breakers. I
>> have no idea whether the breakers were faulty or what, but thought I'd just
>> mention it in case there is a pattern.
>>
>> Best, August
>> Luminalt
>>
>>
>> On Tue, Jan 21, 2020 at 9:10 AM Jason Szumlanski <
>> jason at floridasolardesigngroup.com> wrote:
>>
>>> (System installed by another contractor...)
>>>
>>> I have been tasked with assisting in the investigation of damage in a
>>> subpanel used to combine inverter output circuits (5 strings of
>>> microinverters). There appears to be no damage to conductors or other
>>> system components. It looks like the damage started at the stabs of the bus
>>> bar where the breakers connect. Picture attached. Here are a few clues:
>>>
>>> - Monitoring indicates that damage occurred overnight a few weeks
>>> ago. That night we had rain as a winter front came through Florida,
>>> possibly lightning. The prior day everything was fine.
>>> - The next morning, only 2 of 5 strings started producing power, but
>>> 4 of 5 strings were reporting data to the Envoy. The two strings that were
>>> reporting but not producing power reported 0Vac and Voc on the DC side of
>>> the microinverters.
>>> - A couple of weeks later, 1 of the 2 strings that was producing
>>> power quit doing so, but continued reporting data.
>>> - Customer discovered damage yesterday.
>>> - About a week before the initial damage apparently manifested
>>> itself, another contractor installed a whole house generator transfer
>>> switch on the line side of the PV interconnection. The generator has never
>>> been run (there is not even a LP fuel source on site yet). I pointed out
>>> that the solar interconnection, which was previously on the supply side,
>>> would need to be moved to the supply side of the generator transfer
>>> switch's main breaker before operation. During the transfer switch
>>> installation, the contractor also switched line 1 and line 2, but that
>>> shouldn't really matter, except for Enphase consumption monitoring, which
>>> was messed up by the swapping of the lines.
>>>
>>> So I'm looking for ideas. I'm wondering if the OCPD would be a likely
>>> place for lightning damage to manifest itself. I can't visually detect any
>>> other damage anywhere else. I can't imagine that the transfer switch
>>> installation would have anything to do with it, but the timing is
>>> interesting. Other than replacing the subpanel and OCPD and firing it back
>>> up (no pun intended), I'm not sure how to approach further investigation.
>>>
>>> Jason Szumlanski
>>> Florida Solar Design Group
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200121/3dfd8959/attachment.htm>
More information about the RE-Wrenches
mailing list