[RE-wrenches] Xantrex SW 4048 grid tie mystery
Jerry Shafer
jerrysgarage01 at gmail.com
Sun Dec 22 03:57:20 EST 2019
Well l would start simple and get a sync cable and make sure that they are
al least staying g in correct phasing, then look closely at the
programming, look at the grid voltages and settings, take it out of IEEE
for test purposes only, you might find out you have a board that's out of
calibration causing the issue but start simple
Jerry
On Fri, Dec 20, 2019, 9:44 AM Dave Tedeyan <dtedeyan at taitem.com> wrote:
> Hi All,
>
> I am someone's last ditch effort to get their system working which has
> been non-functional since a few months after installation, 13 years ago...
>
> After getting some new batteries in there, I can at least fire it up. It
> is a grid tie with battery backup situation with two Xantrex SW4048
> inverters. Each inverter is kind of like its own system with two Outback
> MX60 CC's per inverter, and each inverter powers its own 120V backed up
> loads panel. They do not see each other until their 60A single pole
> breakers in the main panel.
>
> What seems to be happening is that after turning on the inverters the AC1
> in good light will flash for about 30 seconds, then it syncs up to the grid
> and the light stays on solid. But then after a little bit, that light will
> start flashing, indicating that the utility power has been dropped, when it
> has not actually been dropped. Then at some point the backed up loads would
> lose power. The customer says that every 1-10 minutes, they would lose the
> backed up loads for 10-90 seconds. This happened all night long until they
> bypassed the inverters.
>
> There are a few other things of note:
> 1. There is a Xantrex GTI for each inverter.
> 2. I see in the manual there is information about stacking the inverters,
> but I am guessing in this setup this not necessary or would even be counter
> productive to stack the inverters. Not sure if the inverters not being
> stacked could cause one of them to unsync with the utility?
> 3. Neutrals and grounds are bonded in their main panel, but also in each
> of the Xantrex DC breaker boxes. I was going to separate them in the DC
> breaker boxes, but found that there is no way to isolate the battery
> negative bus from the box itself, and figured it would be dodgy to unground
> the enclosure. So I am also not sure if the multiple N-G bonds could be
> causing these issues.
>
> Does anyone have any ideas?
> Cheers,
> Dave
>
> *Dave Tedeyan, PE*
> Senior Engineer | Taitem Engineering, PC
>
> 110 South Albany Street | Ithaca, NY 14850
> o. *607.277.1118 x121* f. 607.277.2119
> www.taitem.com
>
> Solar • Sustainability • Energy • Design
> Certified B-Corporation since 2013
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191222/e6a427b6/attachment.htm>
More information about the RE-Wrenches
mailing list