Bill--We enlarge knockouts often. The biggest watch out is if the knock out is close to the enclosure wall, it can be a hassle trying to fit the larger lock nut.It's a little harder trying to drill an offset hole with a step bit, but if there's room, we'll just make a new hole for the larger conduit to fit.
regards, bill

Bill Hennessy
Berks Solar, LLC
371 Centennial Rd
Mertztown, PA 19539

o 610 682 4300
c 484 560 4666
NABCEP certified installer
PA contractor #44411
www.berkssolar.com 

    On Wednesday, December 4, 2019, 10:12:08 AM EST, Jason Szumlanski <jason at floridasolardesigngroup.com> wrote:  
 
 I'm not sure what you're using for raceway, but if using PVC you could come out of the inverter with 3/4 and immediately transition to 1" with a 1"-3/4" PVC adapter. You can get (4) #6 THWN-2 in a 3/4" PVC conduit at 40% fill.
https://www.grainger.com/product/CANTEX-1-x-3-4-PVC-Reducer-4FYK1

Regardless of the conduit type, you could also just pass through a j-box rather than splicing inside. The 3/4" KO should still be big enough for your #6 inverter output circuit.
Jason Szumlanski

|  | 

 |




On Tue, Dec 3, 2019 at 9:05 PM frenergy <frenergy at psln.com> wrote:

  
Wrenchers,
 
            This particular install requires 6 Gauge for the AC output from a few SB7.7......-41 inverters (for voltage drop). Pretty tight for the 3/4" knock-outs in that inverter.  Any harm in using a step-drill to open it up to a 1" KO?  Any experiences with this?  I'm trying to avoid a J-box with a transition to 8 Gauge with 4-14 Polaris connectors.
 
Bill
 Feather River Solar Electric            
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net

 _______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

  
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191204/f648874f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: FRS_working_logo, 50%.JPG
Type: image/jpeg
Size: 8424 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191204/f648874f/attachment.jpe>


More information about the RE-Wrenches mailing list