[RE-wrenches] automatic transfer switches
Jerry Shafer
jerrysgarage01 at gmail.com
Fri Nov 29 00:28:54 EST 2019
Wrenches
Need to be careful here to use something that has the interrupt KVA rating
required to prevent an arc in the event of an under load opening with the
switch proper AIC rating 10,000 or more, last thing I think you want is to
have that kind of liability on products that are not designed for that type
of use. But thats just me.
NABCEP PV Inspector
California Solar contractor
Jerry
On Mon, Nov 25, 2019 at 8:52 PM Bill Hennessy <bill at berkssolar.com> wrote:
> hi folks--
>
> We're installing a grid-tied, battery backup system on a farm where the
> service entrance is on a pole in the yard. At the single-phase, 240v,
> service entrance, there are two main breaker subpanels--one going to the
> house and one to the barn. The buildings are each about 100 feet away from
> the pole in opposite directions. The PV/battery system is located in the
> barn. When utility power is lost and the battery backup kicks in, we are
> looking for a way to bypass the house subpanel at the pole so it won't
> backfeed the grid.
>
> When the grid drops out, we need to tie the backup power coming from the
> barn to the line going to the house. We're thinking an automatic transfer
> switch installed at the pole will do the job, but the transfer switches
> seem to have built in delays to work with starting a generator. The
> switch does not have to be service entrance rated.
>
> It looks like the Asco 300 series has time delay adjustments, but it is
> pricey and has a seven-week lead time. (Thank-you PG&E)
>
> The battery backup system will switch over in milliseconds and we were
> hoping to find something similar for the transfer operation at the pole. We're
> looking for something simple--hopefully a basic transfer switch that will
> quickly switch and drop out when grid power is restored.
>
> Would appreciate any thoughts or suggestions.
>
> regards, bill
>
> Bill Hennessy
> Berks Solar, LLC
> 371 Centennial Rd
> Mertztown, PA 19539
>
> o 610 682 4300
> c 484 560 4666
> NABCEP certified installer
> PA contractor #44411
> www.berkssolar.com
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191128/4a9f4c9c/attachment.htm>
More information about the RE-Wrenches
mailing list