Hi Bill,

We just did something like this with a hydro plant and backup solar site.
We ended up using a Kohler RDT transfer switch with the accessory board.
With the accessory board, its possible to adjust down to about ~1 second
transfer, and without the accessory board, its ~3 second transfer.  The RDT
switch is relatively cheap and well made in various builds.  You just need
to keep the backup inverter voltage output continuously on the emergency
terminals.

Good Luck

On Mon, Nov 25, 2019 at 11:57 PM Jerry Shafer <jerrysgarage01 at gmail.com>
wrote:

> There is the SMA Automatic transfer switch if you go with the SMA battery
> inverter and SMA pv inverter, it can be located seperate of the battery and
> inverter and will take up to 30 kwhrs. of capacity
> Just a thought
>
> On Mon, Nov 25, 2019, 10:52 PM Bill Hennessy <bill at berkssolar.com> wrote:
>
>> hi folks--
>>
>> We're installing a grid-tied, battery backup system on a farm where the
>> service entrance is on a pole in the yard. At the single-phase, 240v,
>> service entrance, there are two main breaker subpanels--one going to the
>> house and one to the barn. The buildings are each about 100 feet away from
>> the pole in opposite directions. The PV/battery system is located in the
>> barn. When utility power is lost and the battery backup kicks in, we are
>> looking for a way to bypass the house subpanel at the pole so it won't
>> backfeed the grid.
>>
>> When the grid drops out, we need to tie the backup power coming from the
>> barn to the line going to the house. We're thinking an automatic transfer
>> switch installed at the pole will do the job, but the transfer switches
>> seem to have built in delays to work with starting a generator. The
>> switch does not have to be service entrance rated.
>>
>> It looks like the Asco 300 series has time delay adjustments, but it is
>> pricey and has a seven-week lead time. (Thank-you PG&E)
>>
>> The battery backup system will switch over in milliseconds and we were
>> hoping to find something similar for the transfer operation at the pole.  We're
>> looking for something simple--hopefully a basic transfer switch that will
>> quickly switch and drop out when grid power is restored.
>>
>> Would appreciate any thoughts or suggestions.
>>
>> regards, bill
>>
>> Bill Hennessy
>> Berks Solar, LLC
>> 371 Centennial Rd
>> Mertztown, PA 19539
>>
>> o 610 682 4300
>> c 484 560 4666
>> NABCEP certified installer
>> PA contractor #44411
>> www.berkssolar.com
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191126/fb72fdd7/attachment.htm>


More information about the RE-Wrenches mailing list