[RE-wrenches] 600V DC contactor

Chris Sparadeo sparadeo.chris at gmail.com
Fri Nov 22 22:47:16 EST 2019


Hi wrenchers,


I am currently on the look out for a DC contactor to suit my needs. A
little background:


Per Sonnen Batterie tech support’s recommendation I have installed a 10 kW
SolarEdge HD Wave inventer coupled with the Sonnen Eco 12. Although the
Sonnen Eco 12 uses an Outback Radian 8kW multimode inverter(of which
Outback suggests to max AC couple input of 5kW) Sonnen says that AC PV
input greater than 8kW will require a contactor  to interrupt a string or
two of the grid interactive inverter so that it’s output will remain less
than the max 8kW input. That’s fine and well, but when asked directly,
Sonnen didn’t have a part # for the contactor and suggested that anything
over 150V DC would be difficult to find. Anyone know of a 600V rated
contactor that would suit the bill? Essentially the contactor would need to
sense grid interruption (via a 15A-AC breaker) and open a 600 V rated DC
string.


I’ve done some preliminary searching and have come up empty handed. Any
input would be greatly appreciated.


Best,


Chris
-- 
Chris Sparadeo


C_802-369-4458
H_802-728-3059
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191122/db402c69/attachment.htm>


More information about the RE-Wrenches mailing list