Hi Aaron,
You may want to install a Combox and enable SD card logging. You can log 5
sec intervals I believe. Be sure to power it off of the Xanbus otherwise
it will turn off with the AC. If you decide this needs to be done, be
ready to sift through a lot of data.
Also, as I recall, the Schneider AGS doesn't automatically decide it should
start the generator if the system goes to LBCO too rapidly. This could
have been addressed in subsequent firmware editions but I remember this. I
suspect that the battery voltage dips enough for LBCO but recovers enough
not to trigger start signal after the AC load is shut off.
I suspect you may be right, that a large load is coming on and driving the
battery below LBCO before the gen start signal can occur. I'd also look
for evidence of corrosion, looking for stiff battery cables. You may try
turning off all the solar when you are there and turning on all the large
loads. Does the battery voltage rapidly crash? If so, do you have some
bad cells? Are the batteries super cold?
I also echo Rays thoughts of not relying on a generator when the place is
unattended to keep pipes from freezing. Most generators will fail under
those circumstances at some point.
Good luck
On Tue, Nov 19, 2019 at 9:40 AM Dave Angelini Offgrid Solar <
offgridsolar at sti.net> wrote:
> Hi Aaron,
>
> I think you have to have higher settings and not let the battery get this
> low for your triggers. I do not know the capacity but you are on the edge.
> When you looked at events, did you look in each device and under faults and
> warning in the system section? Two places right? Really need more data like
> what are the loads. I really doubt this is altitude or temp related.
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
> e-mail offgridsolar at sti.net <offgridsolar at sti.net>
> text 209 813 0060*
>
> On Tue, 19 Nov 2019 07:06:15 -0700, Aaron Mandelkorn <reosolar at gmail.com>
> wrote:
>
> Thanks all for the info. I did check the auto gen start settings and and
> they are set pretty high and at the 15 min, 30 min, and two hr triggers all
> above the LCBO setting of 23v. I have hard time believing that the system
> is crashing at night due to low battery and doing so so quickly that the
> gen isn't coming on. Could this be an issue of temporary voltage drop
> triggering the LCBO due to a large load coming on at night? Why would these
> events not be in the log and why isn't the generator coming on? A seems to
> work during the day and when I come out there to test.
>
> Aaron Mandelkorn
> President / Founder
> Renewable Energy Outfitters
> www.reosolar.com
> Off Grid Depot
> www.offgridnow.com
> 970-596-3744
>
> --
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
--
Mac Lewis
*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191120/8fed8ede/attachment.htm>
More information about the RE-Wrenches
mailing list