[RE-wrenches] More on Supply side connection

Jeff Clearwater jeffc at villagepowerdesign.com
Mon Nov 4 12:33:36 EST 2019


Hey Bill,

Yes that's pretty much it.  Stand-Alone Meter Socket to J-Box with 
Splice Tap to Solar Disco and Main Breaker Panel.  Max backfeed 200 Amps 
(160 Amps rated solar inverters) for single phase.

You'll need to meet the Short Circuit Current Rating (SCCR) for all 
equipment and the IC (Interrupting rating) for all overcurrent 
protection that is required by the particular transformer - service 
entrance circuit.  22kAIC  minimum is usually what is needed to meet a 
200 Amp service supply side connection.

If you have a residential account with PG&E then Greenbook section 6 is 
the equipment you need to meet.
If you have a commercial account with PG&E then Greenbook section 7.

I just proposed to PG&E to use a Eaton (Cooper) B-Line CIR 124TB as 
you'll need test bypass blocks as per the Greenbook for commercial.

I plan to follow Bill Hennesey's advice and use Ilsco Splice Taps for 
the "T" - I plan on using a steel J-box as I'm outdoor in the sun.

Then I feed to an Eaton 200 Amp Heavy Duty Safety Switch for the solar 
with a combined fuse/switch AIC of 200kA

Then I feed also to a Main Panel with a breaker/panel rated to 22 AIK - 
some homeline panels meet this criteria and many standard main breaker 
Square D and Siemens panels can be found for this.

That's it from my end - just submitted this to PG&E this morning and 
will drop by and check with my AJH this week to make sure it all works 
for everyone.

Hope that helps.

Best,

Jeff




I just sent my PG&E proposal

frenergy wrote on 11/4/19 8:01 AM:

> After ruminating on Jeff's inquiry about various ways to do a supply 
> side connection, I came up with the attached drawing. Verbal 
> descriptions are harder for me to wrap my head around. This is in PG&E 
> territory, its 3 phase and I too am trying to avoid the extra cost of 
> higher Amp panels. Please pick it apart.
>
> Thanks,
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191104/3b8e7ac8/attachment.htm>


More information about the RE-Wrenches mailing list