[RE-wrenches] Parts List For AC Couple Disconnect
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Sun Nov 3 13:29:52 EST 2019
Marc, High or low battery cut-out on a battery based inverter is lights
out. There is usually a warning period that becomes a fault. I still think
this is crazy for offgrid unless it is a very large system 20+KW of battery
inverters in a microgrid type mindset with onsight knowledgeable people.
Also lots of DC coupled solar.
Forgive me if I have missed something here as I have installed about 20
gensets for my California wildfire residents last month. Good Luck.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
On Sun, 3 Nov 2019 09:38:51 -0800, Mark Frye <markf at berkeleysolar.com>
wrote:
> Hi William,
>
> Thanks, you bring up issues that are important to me here.
>
> In particular, my situation is that the GT inverter is inter-tied a
> couple sub panels upstream of where I want to put the BB inverter. The
> distance is long, so I am looking for a solution where I don't have to
> run a cable between the two.
>
> In general, I do wonder about using AC line voltage rise to take the Gt
> inverters off line. The main goal is to prevent excess voltage at the
> battery, so monitoring battery voltage is most direct, and there are
> simple solutions for that.
>
> Is AC line voltage a suitable metric for achieving the same goal?
>
> Here is where I could use Wrench knowledge to confirm my thinking, that
> being:
>
> - With excess energy in the system, the charger moves it into the
> battery, raising it's voltage until it reaches it high charging voltage
> set point
>
> - Once the battery reaches it's high voltage set point, the charger
> stops putting energy into the battery
>
> - With no other place to put the excess energy, the AC voltage rises
>
> Am I getting this right, the reason to disconnect AC coupled inverters
> when the battery if full is not to prevent the batteries from being
> overcharged, but rather to prevent the AC line from becoming unstable?
>
> I am hoping this is correct and that with $200 of industrial grade
> devices from Digikey I can implement a robust control that will
> disconnect the GT inverters before the AC line goes so high that the BB
> inverter faults.
>
> Mark
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
>
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
--
More information about the RE-Wrenches
mailing list