[RE-wrenches] Best way to Supply Side connect from a 200 Amp Service Entrance?

Jeff Clearwater jeffc at villagepowerdesign.com
Tue Oct 22 17:24:03 EDT 2019


Esteemed Wrenches,

So from my previous post and research - I think I'm down to the simple 
question of what is the best way to do a supply side connection in PG&E 
territory for a 200 AMP PV feed into a 200 Amp Service.

PG&E won't allow PV circuit wiring to enter their sealed sections.

So how about a simple J-Box like this after a standard 200 Amp Meter 
Socket box?
https://www.ideadigitalcontent.com/files/11028/784572230569_SS.pdf

Then it simply branches to a fusible 200 AMP disconnect for the PV side 
and the other to a standard 200 Amp panel box for the house loads.

I'm feeding 5 SB7.7s so 160 Amps of rated PV x 1.25 = 200 Amps.  right 
at the limit but fully in code and PG&E compliance from what I can tell.

Anything I'm not thinking of?  Easier way to do that "T" connection? 
Existing equipment for 2 200 Amp Breakers off of a single 200 Amp service?

Thanks!

Jeff

Jeff Clearwater wrote on 10/21/19 11:51 AM:

> Hey August, Jay, and Burt and all,
>
> Thanks for the great input! and I'm sorry if I wasn't clearer.
>
> They are not asking for 400 Amps - I suggested it as that was the 
> rating of the solar ready panel I specified.
>
> They are just saying IF it's 400 Amps then they need room for CTs 
> cause it's a shop and hence residential equipment is not approved.
>
> So as August and Glenn indicate below - perhaps the easiest is a 200 
> AMP meter can with a Supply side line.  That does throw it back to my 
> AJH to approve but that is pretty standardI would hope.  It also 
> requires the variance letter from PG&E.
>
> I'm running 5 SB7.7s at 32 Amps each - so 160 AMPS of solar input.
>
> So If I supply a 200 A meter can with supply side lugs that I can feed 
> into a 200 A fused disconnect and solar distribution panel and keep 
> the existing 200 Amp panel box fed by the 200 Amp main breaker - any 
> reason that won't work?
>
> OR does anyone know of a commercial 400 AMP solar ready meter base 
> with 2 200 Amp feeds - one for solar and one for loads that does allow 
> room for CTs?
>
> Thanks,
>
> Jeff
>
> August Goers wrote on 10/17/19 4:35 PM:
>
>> Hi Jeff -
>>
>> PG&E defines the service rating amperage based on the enclosure 
>> rating of the first piece of equipment the service hits. See section 
>> 1.14 in the Greenbook:
>>
>> https://www.pge.com/includes/docs/pdfs/mybusiness/customerservice/startstop/newconstruction/greenbook/servicerequirements/greenbook_manual_full.pdf 
>>
>>
>> This might be why they insist that you need a 400 A service just 
>> because you want a 400 A rated bus. The easy way around it is to 
>> supply a 200 A rated meter socket and main disconnect, then feed a 
>> 400 A sub panel.
>>
>> A meter/main like the Eaton MBEB200BTS might also work for you: 
>> https://www.homedepot.com/p/Eaton-200-Amp-BR-Type-Main-Breaker-Meter-Breaker-without-Distribution-EUSERC-MBEB200BTS/100555147 
>>
>>
>> August
>> Luminalt
>>
>>
>> Hi Jeff,
>>
>> Seems to me if allowed in your jurisdiction, you might be best served 
>> by installing a new 200A fused service disconnect ahead of the 
>> existing main service panel. Or even a 400A one to allow for 
>> additional work inside (CT’s), then perform a supply side connection 
>> in it. Some manufacturers of switchgear have an option for lugs that 
>> accept multiple conductors, so no piercing of conductors needs to happen.
>>
>> Good luck,
>>
>> Glenn
>> On Thu, Oct 17, 2019 at 12:19 PM Jeff Clearwater 
>> <jeffc at villagepowerdesign.com <mailto:jeffc at villagepowerdesign.com>> 
>> wrote:
>>
>>     Esteemed Wrenches,
>>
>>     I am in need of changing out an existing 200 Amp service entrance
>>     in order to accommodate a bus capable of handling a a 200 Amp
>>     Solar backfeed (41 KW system) .
>>
>>     PG&E is upgrading the transformer to handle the backfeed but when
>>     I proposed a Siemens SolarReady 400 Amp service entrance they
>>     couldn't approve it cause since the building is a shop - they
>>     classify it as commercial and require a panel that can handle CTs
>>     when there is a 400 Amp service involved.
>>
>>     Anyone else faced with this have solutions?  What is the cheapest
>>     equipment I can provide to satisfy all requirements?
>>
>>     We don't need to upgrade the existing 200 amp service entrance
>>     equipment for load purposes - only to meet the bus requirements
>>     of backfeed.
>>
>>     Would it be cheaper and easier to use the existing (or new) 200
>>     Amp residential panel - not call it a 400 Amp upgrade but simply
>>     add a 200 Amp Supply Side Connection?  Suggested equipment to do
>>     that in the most economical manner?
>>
>>     Any help well appreciated!
>>
>>     Jeff
>>
>>
>>
>>
>>
>>
>>
>>
>>     -- 
>>     ~~~~~~~~~~~
>>     Jeff Clearwater
>>     Village Power Design
>>     linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
>>     www.villagepowerdesign.com <http://www.villagepowerdesign.com>
>>     cell - 413-559-9763
>>     ~~~~~~~~~~~~~~~~~~~~~~~
>>     _______________________________________________
>>     List sponsored by Redwood Alliance
>>
>>     List Address: RE-wrenches at lists.re-wrenches.org
>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>>     Change listserver email address & settings:
>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>     List-Archive:
>>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>     List rules & etiquette:
>>     www.re-wrenches.org/etiquette.htm
>>     <http://www.re-wrenches.org/etiquette.htm>
>>
>>     Check out or update participant bios:
>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191022/400a91e9/attachment.htm>


More information about the RE-Wrenches mailing list