[RE-wrenches] Running a grid tied system when the grid is down

Harry Mahon Michael.Mahon at sma-america.com
Fri Sep 20 11:27:59 EDT 2019


If using SMA’s Rapid Shutdown System, the SPS function is available as RS is initiated in the manner you described.  If using the TS4 units for 2017 690.12 compliance, the SPS function is not available on the SB US-40.

Each SPS circuit is independent – there is no way for two Sunny Boys to synchronize their SPS waveforms.

One SPS output can be wired to safely power existing circuits to avoid having to swap plug location for loads to be run by SPS. A small 120VAC circuit transfer switch like the unit from Reliance that Goal Zero shows in REIs can do the trick (link below).  The one shown by Goal Zero shows a NEMA 5-15 plug installed but since the SPS can provide 2000W, you would want to hardware the SPS into the similar hardwire Reliance unit rather than the unit with 15A plug. This transfer switch allows homeowners to swap up to four exiting home circuits from grid to SPS power should the grid fail.  The SPS switch for the Sunny Boy is still required in addition to this transfer switch
https://www.goalzero.com/shop/yeti-accessories/yeti-home-integration-kit/

Best regards –
Mike


SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com<http://www.sma-america.com/>

Solar Academy: www.SMA-America.com/partners/sma-solar-academy/overview.html<http://www.sma-america.com/partners/sma-solar-academy/overview.html>

Full training schedule: https://www.sma-america.com/partners/sma-solar-academy/seminars/trainings/training/list.html


[http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/facebook.jpg]<http://www.facebook.com/pages/SMA-America/140290312717395>[http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/twitter.jpg]<http://twitter.com/SMA_America> [http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/wordpress.jpg] <http://www.smainverted.com/>  [Linkedin Logo] <http://www.linkedin.com/company/364675>  [http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/youtube.jpg] <http://www.youtube.com/playlist?list=PL840A5336CAC32332>  [SMAAFORUM_ICON] <http://smaadvance.com/signup/>
[cid:image008.jpg at 01D54D07.DC1BFFF0]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.sma-america.com%2Fhome-systems%2Fpv-solar-and-storage-solutions.html&data=02%7C01%7CMichael.Mahon%40sma-america.com%7Cc4bcd59d55584c70681208d71b72e485%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637008052588484449&sdata=itzAGcXAYe0xd5Zhzjuljm6dijJW%2FRGtItHrvxRkrTI%3D&reserved=0>


This email and any attachments thereto may contain SMA America, LLC confidential, privileged and private material for the sole use of the intended recipient. Any review, copying, or distribution of this email (or any attachments thereto) by others is strictly prohibited. If you are not the intended recipient, please contact the sender immediately and permanently delete the original and any copies of this email and any attachments thereto. Thank you.

From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Dave Tedeyan
Sent: Friday, September 20, 2019 8:52 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Running a grid tied system when the grid is down

Hi Brad,
Not a bad idea with this one to run the loads off the SPS's. Has anyone ever tried wiring these directly into a panel, rather than into an outlet? And do you know if the 120V signal from each one would match up, or do they work independantly? In other words can you wire both SPS into the same panel either on different legs, or on the same leg and use an autoxfr?

And with the Rapid shutdown and SPS. Does it not work with SMA's rapid shutdown box? I thought with those, the grid going down would not affect the rapid shutdown, and that it needs the signal from the controller to initiate RSD. So this way it will continue to work with the grid down.

Cheers,
Dave

Dave Tedeyan, PE
Senior Engineer | Taitem Engineering, PC
[https://www.taitem.com/signatures/logo.png]
110 South Albany Street | Ithaca, NY 14850
o. 607.277.1118 x121  f. 607.277.2119
www.taitem.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.taitem.com&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C47e56e91c6db4419d10308d73dda238b%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637045879462991829&sdata=l%2Fy5ThDRnjZAvBhv46d7F0Jjnj3IXhFgayrS8%2BBNwcE%3D&reserved=0>

Solar • Sustainability • Energy • Design
B-Corporation Best for the World 2018 Honoree


On Fri, Sep 20, 2019 at 10:33 AM Bradley Bassett <bbassett2 at gmail.com<mailto:bbassett2 at gmail.com>> wrote:
If you're not using the SB -40 inverter's rapid shutdown system, it has the SPS Secure Power Supply which does just what your customer wants.

My understanding from talking to inverter mfg, is that trying to do AC coupling with a smaller battery inverters does not work because the anti-islanding in the grid tie inverter will be able to push the frequency off too easily.

Morningstar makes a 600 VDC charge control that has an array transfer switch, so that during an outage you can switch it to use one or two strings to charge a 48 V battery bank and power any 48 V inverter. It is manual so the operator needs to change it back when the power comes back on.

Brad



On Fri, Sep 20, 2019 at 6:41 AM Dave Tedeyan <dtedeyan at taitem.com<mailto:dtedeyan at taitem.com>> wrote:
Hi all,

I get asked this question frequently, as I am sure many others do, and of course the first answer is "it cannot be done". But can it? I have a customer who is very keen on trying to make this happen. After a few lengthy conversations, he still wants to try it, even after understanding the limitations (i.e. a cloud passes by and now you cannot power loads...)

I have some thoughts on how to make this work, and thought I would post it here to get others comments who I am sure have more experience in something like this than I do.

-PV system would have to be backfed, so that they can turn off the main breaker to disconnect from the utility entirely (and then have to look at the neighbors, or guess when the grid comes back)
-Have a fairly small 12V off grid inverter/charger than can be powered by a single 12v battery. This inverter would have to be manually turned off until after the grid is down and the main breaker is disconnected.
-Would also need an auto transformer to bump up the voltage to 240V. Something like the Outback PSX240.
-Once the main breaker is off and the off grid inverter is on, would it be able to wake up the grid tied inverters? On this project, there are two SMA SB-40 inverters.
-There would need to be some kind of dump/diversion load to deal with excess power coming from the GT inverters. I have not used these in the past, but are the controllers smart enough to just deal with any excess power in the system?
-Have a trickle charger on the battery to keep it topped off most of the time.

-Another thought would be to DC couple. This would involve having a DC switch in one of the strings going to the GT inverter, such that when the house is islanded from the grid, they can flip the switch and have that one string go to a high voltage CC. Then they could just run some small loads off the power from that one string, or maybe we could allow it to try to wake up the GT inverters as well.

This particular homeowner specifically does not want much in the way of batteries and has a smaller budget than will allow something sensible like a Sunny Island.

At least in upstate NY, there are many people who would like to be able to take advantage of their solar when the sun is shining, but who just do not have the budget for a legit battery system. I am somewhat surprised that there is no simple industry solution for this yet, although maybe it is more complicated than I am making it out to be. And of course, you need a very hands on homeowner who very well understands the limitations of this kind of setup.

I would certainly appreciate any feedback or comments on this, and also would like to hear if anyone has tried this kind of setup before.

Thanks much!
-Dave

Dave Tedeyan, PE
Senior Engineer | Taitem Engineering, PC
[https://www.taitem.com/signatures/logo.png]
110 South Albany Street | Ithaca, NY 14850
o. 607.277.1118 x121  f. 607.277.2119
www.taitem.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.taitem.com&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C47e56e91c6db4419d10308d73dda238b%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637045879462991829&sdata=l%2Fy5ThDRnjZAvBhv46d7F0Jjnj3IXhFgayrS8%2BBNwcE%3D&reserved=0>

Solar • Sustainability • Energy • Design
B-Corporation Best for the World 2018 Honoree
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C47e56e91c6db4419d10308d73dda238b%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637045879463001825&sdata=%2BCv9Z3dxZDdpN59SX6V1H7e8gA83N0CiXH77ggEUy6Y%3D&reserved=0>

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C47e56e91c6db4419d10308d73dda238b%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637045879463001825&sdata=UbwE%2FH3YnQhsLVYgmlMEM%2B0srnjHmvVeae4Md5bPuvE%3D&reserved=0>

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C47e56e91c6db4419d10308d73dda238b%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637045879463001825&sdata=QRIpVK2kvigjt6A1i%2FzGkGey4AuhfqiC%2FEJypnMaN4o%3D&reserved=0>

Check out or update participant bios:
www.members.re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.members.re-wrenches.org&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C47e56e91c6db4419d10308d73dda238b%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637045879463011825&sdata=cxwHL2Y0mDXDer3aQc8CJUwdlD0CQqbe355yTRBVv3U%3D&reserved=0>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C47e56e91c6db4419d10308d73dda238b%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637045879463011825&sdata=ymH8G%2FagBctKkdHuHk2eMZ8ZEmQvaFluoFIZzZ2cD6o%3D&reserved=0>

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C47e56e91c6db4419d10308d73dda238b%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637045879463021816&sdata=GoWWsvElHHFJOdpVMFIYoF1fYQUphQZLS8xhPRIfDBM%3D&reserved=0>

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C47e56e91c6db4419d10308d73dda238b%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637045879463021816&sdata=zDftLMSp%2FoTmCqqtkqBVD5SikS4yj%2B%2BOSIsCRtTUerg%3D&reserved=0>

Check out or update participant bios:
www.members.re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.members.re-wrenches.org&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C47e56e91c6db4419d10308d73dda238b%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637045879463031809&sdata=2OseHDYW%2FGVHdPQ5OEGEI1nncDHRfwwCZ9%2FRM5NlVQ4%3D&reserved=0>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190920/4fa15600/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 428 bytes
Desc: image001.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190920/4fa15600/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 428 bytes
Desc: image002.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190920/4fa15600/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 717 bytes
Desc: image003.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190920/4fa15600/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 731 bytes
Desc: image004.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190920/4fa15600/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 480 bytes
Desc: image005.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190920/4fa15600/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 808 bytes
Desc: image006.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190920/4fa15600/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 22585 bytes
Desc: image007.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190920/4fa15600/attachment-0005.jpg>


More information about the RE-Wrenches mailing list