[RE-wrenches] SMA phantom arc faults
Jeff Clearwater
jeffc at villagepowerdesign.com
Sun Sep 15 20:54:52 EDT 2019
I did finally get it to clear using taps but it was a lot of tapping. 3
taps after the second restart with blue light blinking did it - or maybe
that was a coincidence - and it just decided to clear then.
Bill - I did try clearing it through the Data Manager M (EnnexOS) but
there didn't appear to be any place to clear it - nor update the
firmware either that I could find.
I was in the process of logging into the machine itself onsite when I
tried the taps - good thing cause I misplaced the installer log-in! Next
step was PUK - yuk!
And the "source" of the arc-fault was not wiring or connectors - it was
I had turned on and off the DC disconnect as I was making sure Neurio
worked - a guick on and off again inadvertently (changed my mind
midstream as to which I wanted) That was enough to trip the arc-fault!
SMA if you are listening - can't you make this a bit easier? Having to
reset passwords by contacting SMA - that's a major on top of all the
arc-fault pain we are feeling!
Thanks all,
Jeff
frenergy wrote on 9/15/19 8:38 PM:
> I've only had the "tapping" method work on SB-22 inverters, not on -40
> inverters. You gotta log on to the machine which I think you can only
> do onsite. Has anyone ever done a reset of the 8206 from the portal?
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
> On 9/15/2019 12:36 PM, Jeff Clearwater wrote:
>> Hey Folks,
>>
>> How do you clear an 8206 from a SB7.7-US? the manual says tap on the
>> cover within 10 seconds of error message. That's not working.
>>
>> Does that tap then set it up for the next restart or is it supposed
>> to clear it right away - I've tried restarting again to no avail.
>>
>> When I tap right after the message appears it simply toggles to the
>> next screen.
>>
>> Jeff Clearwater
>> Village Power Design
>>
>> Mac Lewis wrote on 9/6/19 7:14 AM:
>>
>>> Hello Wrenches,
>>>
>>> You may be aware of this but the -92R firmware supposedly has
>>> addressed the arc fault issue for the US-40 inverters. See here for
>>> the download:
>>> https://www.sma-america.com/service-support/downloads.html It fixed
>>> an arc fault issue for me yesterday at least. Bring a thumb drive,
>>> the update process took about an hour to perform.
>>>
>>> On Tue, Sep 3, 2019 at 10:40 AM Dave Angelini Offgrid Solar
>>> <offgridsolar at sti.net <mailto:offgridsolar at sti.net>> wrote:
>>>
>>> Same up here in the southern sierra. I get calls from ABB and a
>>> few from SMA to look at systems that people far away installed
>>> and as a local 3rd party it can save some money. Whatever they
>>> quote me I triple the price. 1/3 up front and the rest when it
>>> is done. ABB is really slow with payment. I think they sold
>>> their inverter business? Sunpower is a great panel but they have
>>> had some bad runs. Probably why there are so many new/used
>>> panels on the secondary market. They are great for Offgrid
>>> ground arrays and no AFD.
>>>
>>> On Tue, 3 Sep 2019 09:52:19 -0400, Dave Tedeyan
>>> <dtedeyan at taitem.com <mailto:dtedeyan at taitem.com>> wrote:
>>>
>>>> Chris,
>>>> Sunpower has taken some responsibility on some of our older
>>>> Sunpower systems that are arc faulting. We tell them that a
>>>> system is arc faulting, and then they insist on sending up a
>>>> 3rd party contractor to inspect the system and potentially
>>>> install what they call "Tigo Diodes". I am still not exactly
>>>> sure what that is. It also seems to take them months to send
>>>> anyone to upstate NY, as we have a bunch of customers that have
>>>> been waiting months for the 3rd party contractor to come take a
>>>> look. You likely could only follow this route though if the
>>>> system was installed by a Sunpower dealer and you are a
>>>> Sunpower dealer yourself. If the original system was from a
>>>> Sunpower dealer, you can also have the customer call Sunpower
>>>> directly.
>>>> Cheers,
>>>> Dave
>>>> *Dave Tedeyan, PE*
>>>> Senior Engineer | Taitem Engineering, PC
>>>>
>>>> 110 South Albany Street | Ithaca, NY 14850
>>>> o. 607.277.1118 x121 f. 607.277.2119
>>>> www.taitem.com <http://www.taitem.com>
>>>>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
>
>
> ------------------------------------------------------------------------
> Avast logo <https://www.avast.com/antivirus>
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com <https://www.avast.com/antivirus>
>
>
> <#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190915/b5974d3b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 200 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190915/b5974d3b/attachment.png>
More information about the RE-Wrenches
mailing list