Outback inverters can do that, start and stop the genny, start up if loads
are above a programmed setting. I have used Lutron for a similar
application that turned one AC on at a time. You can use the inverter to
turn off load(s) if they is/are to high, it's all programable
Jerry
On Wed, Sep 11, 2019, 2:42 PM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:
> In an off-grid situation I'm looking for a strategy to manage transfer
> from generator power to inverter power because I have a lot of high startup
> load appliances planned for a system. Think 8 mini-refrigerators, one sub-z
> large refrigerator, and an under-cabinet ice maker, not to mention air
> conditioning. I would like to start these loads in stages if they all call
> to start up immediately upon system startup or during ATS switch over. Any
> ideas?
>
> I guess while I'm on the subject I should ask about my eye-roll,
> keep-me-up-a-night, giving-me-heartburn problem with this ice maker. It's
> going to be outdoors in Florida and they expect it to make 25-50 pounds of
> ice per day. I am finding it really hard to estimate energy use for this
> appliance. Any ideas (other than the obvious "don't do it" answer)?
>
>
> Jason Szumlanski
> Florida Solar Design Group
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190912/9e35ef3f/attachment.htm>
More information about the RE-Wrenches
mailing list