[RE-wrenches] connector mismatch

Ray ray at solarray.com
Tue Sep 10 11:12:07 EDT 2019


Has anyone noticed whether the location in the string or the array 
voltage makes a difference in the failures?  Is this more an issue at 
higher array voltages (>600 v) and at points in the array that the 
voltage would be highest?  We primarily do low voltage (<200 v)  off 
grid systems, and have not seen any failures.  But I'm wondering if we 
need to go back and start looking for issues, as I can't promise that 
every module connector matched the connectors we used, especially if as 
has been reported, some manus used different connectors for neg and pos.

To further the problems, I've personally replaced what looked to be 
counterfeit connectors on cheap 12 v modules. The connecting metal was 
obviously inferior: very malleable and made such a poor connection that 
it created an open circuit.  Luckily this was at 20 v, and no melt down 
occurred. Also Luckily, I didn't provide the module.

Ray Walters
Remote Solar
303 505-8760

On 9/4/19 4:26 PM, Jerry Shafer wrote:
> Just to add, l had a lab and l did testing on connectors, we found 
> that most of the aec issues were under low light. This appeared to be 
> when iradiance was low and once the irads went up the issue was less 
> likely, this was because the Male-female contact was not tight enough 
> and under lower power it would arc instead of heating up and 
> expanding. I used a IR Camera but could see little change due to the 
> plastic.
> Then l used an IV curve tester and shaded partially shaded the module 
> after several repeat testing the connectors got warm. I would suggest 
> making your own connector pull out tool to check the contact 
> pressures. This is where you may find your problem components. It 
> appears that early am testing had lower volts and the inverter pushed 
> the current up and causes the loose connector to fail due to the lower 
> volts.
> This testing was done both in the field 1/2 meg and lab testing 
> results were very close.
> The modules used for testing were Trina and the field inverters were 
> ABB and Fronius
> Sorry for the long note
> Jerry
>
> On Wed, Sep 4, 2019, 2:52 PM Steven Lawrence <lawrencesteven at gmail.com 
> <mailto:lawrencesteven at gmail.com>> wrote:
>
>     Everyone,
>
>     Just to add to this, I've seen multiple melted connectors that
>     couldn't be traced to anything other than mixing manufacturers. 
>     I've seen some connectors where you can clearly seeing arcing on
>     the pin itself and nowhere else.  The crimps and the housing were
>     fine.  I've postulated it had to do with slightly different metals
>     expanding/contracting at different rates.  I've made it a very
>     hard rule at my company to never mix manufacturers of connectors. 
>     When we order modules, we specifically have the PO call out the
>     manufacturer of the connector (can't just be "MC4 compatible"). 
>     Typically we order that same brand of connectors, but sometimes we
>     end up getting 6" jumpers made by a harness company (there are
>     some connectors out there that can only work with #12 wire. Can't
>     use them on #10 homeruns).  It's drastically cut down on the
>     number of melted connectors.  We've averaged maybe 1 or 2 on 6MW
>     projects over a year with this hard requirement versus 100+ we had
>     on a 1MW rooftop project that mixed multiple manufacturers.
>
>     Steven Lawrence
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out or update participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190910/d27ec856/attachment.htm>


More information about the RE-Wrenches mailing list