[RE-wrenches] Large off-grid inverter/storage
David Katz
dkatz at backwoodssolar.com
Thu Sep 5 22:50:29 EDT 2019
The sentence “25KW per hour“ does not make sense. Do they mean 25KWh per
hour? That would be 600 KWh per day! That would require over 200KW of PV.
David Katz
On Thu, Sep 5, 2019 at 3:33 PM Dave Angelini Offgrid Solar <
offgridsolar at sti.net> wrote:
> I often find that numbers like 25KW per hour are just overblown and the
> rest of the Offgrid load power data is too high.
>
> Offgrid is all about the state of the art in not needing high power levels
> by using the best equipment available for the loads.
>
> One can't simply take a power bill from a utility and try to duplicate it
> offgrid. The loads have to be reduced drastically.
>
> Maybe this is not the case here and if so I digress. Good Luck
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
> e-mail offgridsolar at sti.net <offgridsolar at sti.net>
> text 209 813 0060*
>
> On Thu, 5 Sep 2019 16:16:27 -0600, "Dana" <dana at solarwork.com> wrote:
>
> You will have to park the ‘Package’ somewhere… Yeah off grid takes space &
> WLA batteries like to be warm in the winter & not too hot in the summer.
>
> Basements? Dedicated building? Storage container [insulated]?
>
> Radiant floors make for happy batteries. Cool in summer & warm in winter.
>
>
>
>
>
>
>
> Dana Orzel Great Solar Works, Inc.
>
> *C - 208.721.7003 dana at solarwork.com
> <dana at solarwork.com>*
>
> Idaho Contractor - # 028765 Idaho PV # 028374
>
> NABCEP # 051112-136 www.solarwork.com
>
> "Responsible Technologies for Responsible People since 1988"
>
> *P* Please consider the environment before printing this email.
>
>
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Andrew
> *Sent:* Thursday, September 05, 2019 3:15 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* [RE-wrenches] Large off-grid inverter/storage
>
>
>
> Hey Everyone,
>
> I have been recently been getting more and more inquiries
> for some quite large off-grid sytems(25kw per hour) and seeing what you
> guys have for suggestions on bigger inverters and storage systems? I could
> do 2 triple stack Schneider’s and a bunch of HUPS industrial batteries but
> it all just takes up so much space and I know there are some other
> companies out there with package units. Thoughts?
>
>
>
> Andrew Perkins
>
> Greenwired
>
> P: 707-923-2001 ext. 100
>
> 1150 #1 Evergreen Rd
>
> Redway, CA 95560
>
> www.greenwired.com
>
> [image: Description: signature]
>
>
>
> --
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> --
David Katz Sent from Gmail Mobile
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190905/b3e4cd51/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 8628 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190905/b3e4cd51/attachment.png>
More information about the RE-Wrenches
mailing list