[RE-wrenches] 30 amp disconnect/40 amp breaker
Brian Mehalic
brian at solarenergy.org
Wed Aug 21 20:44:43 EDT 2019
I agree Blake - you have to check the specs and consult the mfg. The same is true with combiners, some are rated for continuous duty/full load, and some are not. Lots of large systems out there with 200A combiners connected to 250A OCPDs (and 250A conductors, but that’s another story...).
Brian
> On Aug 21, 2019, at 5:20 PM, Blake Gleason <blake at sunlightandpower.com> wrote:
>
> Typically a fused disconnect can only handle 80% of it's nominal current on a continuous basis. Unfused disconnects are often 100% rated. For example, see attached Square D bulletin #3110DB0401R0410.
>
> So, a 100% rated (unfused) 30A disconnect (at least, from Square D) should be fine here, as long as your OCPD is provided elsewhere (eg, the breaker you mentioned).
>
> NEC 690.8(B)(1)(Exception) explicitly allows a 100%-rated device to be used without multiplying the inverter output current by 125%.
>
>
>> On Wed, Aug 21, 2019 at 3:22 PM Greg <greg at remotepowerinc.com> wrote:
>> Fellow Wrenches, I'm having a discussion with a utility engineer regarding the following situation:
>>
>> Installing a 6kW inverter that has a full rated output of 25 amps. 80% of 30 is 24. That means to me I need to go up to a 40 amp breaker. I'm running #8 (continuous load 25 x 1.25 etc.)
>> The engineer believes I should use a 60 amp disco since it's on a 40 amp breaker. My thinking is I can use a 30 amp disco since it can not produce more than 25 amps ever.
>>
>> Do any of you have a reference that shows what I'm doing is okay? Not okay?
>>
>> Thanks again,
>> Greg Egan
>> Remote Power Inc.
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
>
> --
>
>
>
> Blake Gleason, PE | Employee-Owner |
> Director of Innovation & Technical Excellence
>
> 510.845.2997 x128
>
> Follow us on Facebook, LinkedIn or our website.
>
> <Square-D-Switch-PV-Bulletin_06-10_100percent_rated.pdf>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190821/822f4b52/attachment.htm>
More information about the RE-Wrenches
mailing list